correct wire size again !!

hairyjrDecember 9, 2010

We have found a new oven and I believe it might work. We have 240v on 10-3 wire with 30 amp breakers.The new oven specs are; total connected load: 6.8KW @ 240v, amp rating at 240v-30amp. Will this work?? Thanks for the help to anyone that answers.

Thank you for reporting this comment. Undo
kurto

Yes, assuming that it's copper wire, everything should be fine. 6.8kw converts to 28.3A.

    Bookmark   December 9, 2010 at 9:00PM
Thank you for reporting this comment. Undo
DavidR

You will want to check the oven's installation instructions to make sure that a 30 amp breaker / circuit is called for.

    Bookmark   December 9, 2010 at 10:10PM
Thank you for reporting this comment. Undo
brickeyee

"Yes, assuming that it's copper wire, everything should be fine. 6.8kw converts to 28.3A."

Except that would load a 30 amp circuit to over 94%.

It might be acceptable if the installation instructions call for a 30 amp circuit, otherwise you may need a little more.

    Bookmark   December 10, 2010 at 9:42AM
Sign Up to comment
More Discussions
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
© 2015 Houzz Inc. Houzz® The new way to design your home™