I have a hot tub that is wired with 6 gauge/4 wire. The 50A breaker is not in a covenant location, so I want to put a simple light switch between the breaker and the hot tub to turn it on and off. What do I need to go this? I guess the first question is, Can you do this?

Thanks.

Thank you for reporting this comment. Undo
mike_kaiser_gw

Absolutely not. Whatever device you introduce into the circuit needs to also be rated for 50 amps. Ordinary wall switches are rated at 15 or 20 amps.

Are you planning on putting this switch in the house and it needs to look attractive? Or can you get away with a simple metal box, similar to, say, a disconnect for an air conditioning unit?

    Bookmark   December 24, 2011 at 7:04AM
Thank you for reporting this comment. Undo
Ron Natalie

As Mike points out a switch will NOT handle the load. You can get outdoor rated disconnects/switches that you could use. In fact you SHOULD have one in sight of the part of the tub with the maintenance access.

    Bookmark   December 24, 2011 at 8:49AM
Thank you for reporting this comment. Undo
ccorwin15

Mike, Yes, we want it to be attractive, The hot tub is a single person tub that we put in a bathroom. I was hoping that there was a converter of sorts that could break the 240v circuit with a simple light switch.
Thanks.

    Bookmark   December 24, 2011 at 1:19PM
Thank you for reporting this comment. Undo
hexus

It can be done via other means though. If you wanted to use a simple run of the mill switch to do this, it is going to be expensive.
You would need to get a contactor with a 120v coil.

    Bookmark   December 24, 2011 at 3:01PM
Thank you for reporting this comment. Undo
ccorwin15

Hexus, Could you explain more about how the contractor would work? Thanks.

    Bookmark   December 24, 2011 at 4:11PM
Thank you for reporting this comment. Undo
hexus

contactor, not contractor

You would wire the contactor to make/break power feeding the hot tub. A normal run of the mill switch could be used to energize/de-energize the coil.

If you have no experience with this sort of thing you should get someone who does to help you. The only reason I brought it up is because you could do what you want by this means.

    Bookmark   December 24, 2011 at 6:57PM
Thank you for reporting this comment. Undo
petey_racer

You MUST have a service disconnect with sight of the tub. Why not use that?

    Bookmark   December 24, 2011 at 8:22PM
Thank you for reporting this comment. Undo
petey_racer

By this I mean must as in required, not must as in "probably".

    Bookmark   December 24, 2011 at 8:23PM
Thank you for reporting this comment. Undo
ccorwin15

Hexus, Thanks. I will check with the electrician who install my breaker panel. Petey, Do you need a service disconnect if the tub sits empty except when its being used. What we have, is a Japanese soaking tub that has a hot tub system installed in it. So it has a drain. We found it at a yard sale. It is a one person tub and installed in the bathroom. Does it require the service panel because of the heating unit? Other then that, its the same as a jetted tub.

    Bookmark   December 25, 2011 at 10:04AM
Thank you for reporting this comment. Undo
mike_kaiser_gw

I'm guessing here so correct me if I'm wrong. Rather that using the existing tub controls that likely maintain a water temperature, you want to turn this hot tub "off" when not in use.

Since an ordinary wall switch isn't rated for the amperage of the circuit, you'd need to introduce a contactor into the mix. Contactors are essentially electrically controlled switches. You'd need a 2-pole contactor rated at 60 amps with a 120v coil. When you flip the wall switch the contactor would close allowing electricity to flow to the hot tub. You'd likely need some kind of enclosure and a place to mount it, keeping electrical codes in mind.

    Bookmark   December 25, 2011 at 10:08AM
Thank you for reporting this comment. Undo
petey_racer

ccorwin15, a service disconnect is required for service, maintenance and safety. It has nothing to do with whether it has water or people in it.

    Bookmark   December 25, 2011 at 10:49AM
Thank you for reporting this comment. Undo
hexus

If you were to mount the switch for the contactor within sight if would serve as the disconnecting means.
It's all the same thing, it will just look a lot nicer which is what I thought the main goal of all this was?

    Bookmark   December 25, 2011 at 12:46PM
Thank you for reporting this comment. Undo
ccorwin15

Thank you all for all your help!

    Bookmark   December 25, 2011 at 6:22PM
Sign Up to comment
More Discussions
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Two fans on same circuit in different rooms, can't get wiring right
So here's the situation. I have two ceiling fan/lights...
jenfarino
Sponsored Products
WLF series High Power LED Waterproof Light Bar Fixture
Super Bright LEDs
Ariadni Incandescent Light Dimmer by Lutron
$19.00 | Lumens
Single Stem Vase
$9.99 | Dot & Bo
Fat Cat 3 in 1 Flip Game Table Multicolor - 64-1049
$650.00 | Hayneedle
Earthwise Cordless Self-Propelled Lawnmower
$419.00 | FRONTGATE
Scroll Chair Slipcover
Overstock.com
Barn Bronze 12" High Solar LED Outdoor Wall Light
$89.00 | Lamps Plus
Everest Geometrics Tan Rectangular: 5 ft. 3 in. x 7 ft. 6 in. Rug
$299.00 | Bellacor
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™