electrical Install and code questions

cdcliveDecember 7, 2012

I am wanting to run power to a new shed/workshop in the back yard. I live near Seattle and permit/inspection is through Washington L&I enforcing 2008 NEC.

My plan currently includes:
1) Replace 4 standard 15 amp breakers with 2 tandem breakers. The panel allows this, but not sure if code requires AFCI). Fill void with 20 amp 2 pole breaker.
2) Use existing (but disconnected) 4 wire 6 gauge running through 1.25" conduit in the crawlspace to route a multi wire circuit to GFCI protected disconnect box located outside the house.
3) Connect 12/3 underground cable to the disconnect box, conceal it in conduit to get it underground, route it to the out building and up through the sill plate to a double pole disconnect switch in the shed from which I will distribute it to receptacles and a wall heater

I would love feedback or suggestions.

Thanks,

CDC

Thank you for reporting this comment. Undo
Ron Natalie

Most likely you can get away without upgrading to AFCI just because you're scrunching breakers down. However it's up to the AHJ. Unfortunately, I don't think I've ever seen a tandem/skinny AFCI breaker if it comes to that.

Given one multi wire circuit here you can get away with what you are doing without installing a grounding system at the outbuilding.

Are we talking about one of those spa packs? (GFCI disconnect things). Why bother? You could just put a GFCI breaker in the panel or a GFCI receptacle in the outbuilding.

    Bookmark   December 7, 2012 at 7:50PM
Thank you for reporting this comment. Undo
cdclive

Ronnatalie, thanks for your input. I don't think they make tandem AFCI breaker either. I'm hoping they consider what I'm doing simple replacement and let it slide otherwise my plan goes out the window.

Your right, the existing wire was (I assume) connected to a hot tub. The spa is gone but all the wiring and the disconnect box stayed. They only reason I'd use it is because it's already here.

A couple potential problems I forgot in my earlier post:
The existing wires are all black with tape to color code the ends. I'm not sure if that is still allowed. And the conduit is just sitting on the ground of the crawl space, not secured to the walls or joists. It's less then a crawl space, more of a belly slide space, but I think they may make me do something there.

    Bookmark   December 7, 2012 at 10:16PM
Thank you for reporting this comment. Undo
Ron Natalie

It's not legal now nor has it been legal for a very long time to mark #6 black wire white or green to designate ground or neutral conductors. You don't have a legal installation now, nor was it likely legal at the time the hot tub was installed.

    Bookmark   December 8, 2012 at 8:57AM
Thank you for reporting this comment. Undo
cdclive

Thanks Ronnatalie. That is a great thing to know in advance. I won't mess around with trying to save time/money by using the existing set up and will just run new 12/3 cable through the crawl space.

Please post any other advice you may, otherwise I'll update after the first inspection.

    Bookmark   December 9, 2012 at 5:59PM
Sign Up to comment
More Discussions
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™