Sub Pannel Questions....

richjsnDecember 9, 2009

I am building a workshop for my attached garage and in the process of running electrical wiring before I insulate and drywall. I have talked to two different "home depot" electric guys and have some confusion so let me set up what I am planning on doing. I ran a 6/3 w/ground from my main panel to the garage (70 feet $$). On the main panel in my basement I am going to install a 60amp breaker for that line (240v). That line goes to the new subpanel in the garage. In the subpanel if I am correct I donÂt need a main breaker since it is an attached garage. I am running three lines from the subpanel all 240v. One for a Heater, one for a table saw, and one for future use. Heater is a 30amp breaker 10/3 wire. Table saw is a 20 amp breaker 12/3 wire. I think for now I will just run conduit to an outlet for the future one. Question... am I limited on the amount of amps with that wire? The sub panel will have a neutral and a separated ground bar. Not sure since it is a garage if I need to use GFI breakers in the subpanel. Does this all sound right?

Thanks to all in advance.

Thank you for reporting this comment. Undo
bigbird_1

Heater requires 10/2, not 10/3. Table saw is also 12/2. Anything drawing 240V does not require a neutral.
Local codes determine if you need a disconnect at the sub. I'm in Canada so not sure if you need GFCI's in the garage. In Canada we don't. If you do, you can use GFCI receptacles.
"Question... am I limited on the amount of amps with that wire?"
What wire are you referring to? Any wire is limited with respect to its ampacity by the wire gauge and by electrical code.

    Bookmark   December 9, 2009 at 6:40PM
Thank you for reporting this comment. Undo
richjsn

Quick reply thanks...I can use any wire if I install the correct conduit. More concerned if I am limited in amps by the sub pannel and the 60amp breaker in the main.

    Bookmark   December 9, 2009 at 6:43PM
Thank you for reporting this comment. Undo
bigbird_1

It's generally a lot easier and somewhat cheaper to run individual THWN/THNN wires in conduit rather than cable. The subpanel total amps (if you add up all the breakers in the sub) is inconsequential. All that matters is that the total amps being drawn at any one time does not exceed the supply capacity. If you're feeding the sub with a 60A breaker, the 60A breaker will trip if you try to draw more than 60A at any one time. A 6/3 feeder requires a max 60A double pole breaker. Any larger breaker will be non code compliant as well as dangerous.

    Bookmark   December 9, 2009 at 7:22PM
Thank you for reporting this comment. Undo
fotostat

"I ran a 6/3 w/ground from my main panel to the garage"

What type of cable did you run?

You might only be able to use a 50Amp breaker, depending on the cable.

    Bookmark   December 12, 2009 at 10:40AM
Sign Up to comment
More Discussions
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™