I'm a little hesitant to post, since I feel like I really should know this answer, but is it within code to come off a panel with a receptacle branch, say on the garage wall where the panel is located, then have one NM conductor feeding a few boxes down the wall in one direction while the rest are fed from a separate NM conductor leaving the same box in the other direction. I feel like I should be able to point to a specific reason why you should or should not be able to have two non-switched load paths leaving a box like this, but I've just not had a reason to tee off a branch with anything other than a switched load in so long. I know it'll work and I know it CAN be done safely (so can base jumpint..) but I can't remember if it's against NEC or not.

Thanks.

Dan

Thank you for reporting this comment. Undo
Ron Natalie

T's are allowed. There's no specific requirement to daisy chain things. Be careful not to exceed the box fill on the box you're teeing from. Don't forget that 120V receptacles in garages that are at or below grade require GFCI and you need to make sure that if you're using a GFCI receptacle that it is correctly placed in the circuit to protect the rest.

    Bookmark   December 20, 2011 at 4:43PM
Thank you for reporting this comment. Undo
brickeyee

Some breakers are even rated to have two wires landed on the breaker.

It might be easier to put a GFCI receptacle in the first box on each side, then wire the rest on that side from the LOAD side of the GFCI receptacle using conventional receptacles.

    Bookmark   December 20, 2011 at 7:34PM
Thank you for reporting this comment. Undo
dgeist

Putting the T at the first box was what I was thinking with the loads feeding off it, but it would definitely have to be a 20A GFCI receptacle if so. Do standard GFCIs have load-side (i.e. protected) terminals or will I need to get a GCFI breaker?

    Bookmark   December 20, 2011 at 8:57PM
Thank you for reporting this comment. Undo
dgeist

Nevermind that last question. Of course they have protected load side terminals...

    Bookmark   December 20, 2011 at 9:43PM
Sign Up to comment
More Discussions
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™