2 ovens 240/20 & 240/30 on 1 line 240/50

l1234December 11, 2009

I have two ovens (Miele h4080 240/20 and H4880 240/30). They are not a single combo, but have two separate wips. I have wall open to studs and do not know what to wire.

My preferred way would be to run #6 240/50 4-wire line and connect two receptacles. What the code requires. Do I have to run 2 separate lines? Had these ovens were a factory combo - they would have 1 plug, but they do not make a combo like that with these two?

If I can have one 240/50 line - how do I connect two receptacles or does a dual receptacle exists for #6 cable?

Thank you for reporting this comment. Undo
bigbird_1

Each appliance must be on its own dedicated circuit. How would you have overcurrent protection for the 20A and separate 30A appliances with a 60A breaker?

    Bookmark   December 11, 2009 at 4:34PM
Thank you for reporting this comment. Undo
l1234

Sounds logical - but I think over-current protection is more for the circuit wire than for the appliance. Appliances usually have their own over-current protection. On the other hand when there is double oven combo unit comprising 2x 30A ovens it operates on a single 60A circuit panel breaker protecting single line.
Confusing enough - forget logic forget physics - what the law requires?

    Bookmark   December 11, 2009 at 5:25PM
Thank you for reporting this comment. Undo
bigbird_1

Sounds logical to me. I don't have a code book nearby. Hopefully someone else can comment on code requirement.

    Bookmark   December 11, 2009 at 5:58PM
Thank you for reporting this comment. Undo
brickeyee

What do the installation instructions for the ovens say?

If they say 'require' for a separate circuit, the NEC says you must follow the manufacturer's instructions.

The issue is is the appliance wiring sufficient to carry a fault current to trip the larger breaker?

The internal wiring needs to be able to carry at least the breaker rating to avoid the appliance conductors acting as a fuse before the breaker can trip.

    Bookmark   December 12, 2009 at 10:16AM
Sign Up to comment
More Discussions
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Same circuit for AC air handler and whole-house fan?
Hi, I've got a furnace/air handler in my attic. I was...
elofgren
Swimming pool wiring
I have 2 gfci circuits operating two pool pumps. Is...
dalemd88
Sponsored Products
Emerald Home Berkeley Cocktail Table - T140-0
$213.44 | Hayneedle
Turquoise Sofa - TURQUOISE
$4,499.00 | Horchow
National Public Seating Science Lab Table 36 Inch H - Chem-Res Top - Plain Front
Beyond Stores
Resident | Felix Chair
YLiving.com
Reflection Giclee Glow 16" Wide Pendant Light
Lamps Plus
Roll & Hill | Agnes Chandelier - 6 Light
YLighting
Samsung Galaxy III Power Case
$69.95 | FRONTGATE
Furniture of America Alodie Leatherette Dining Chairs (Set of 2)
Overstock.com
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™