Hey everyone, I have a Briggs 8KW 10KW generator with a reliance 10 circuit transfer box that I plan to power most of my house with. My question/problem is the place that is best for the generator is 100ft away from the transfer box. Here is what is easiest, but I'm guessing is not best? I could just get a 100ft 10 gauge 4 prong (240/30amp) cable and run it right to the transfer box from the gen. Would this have too much loss for proper use? If I were to run the input box it would still be 50ft of 10/3 inside the house and then another 50ft of plug. If I use 8/3 on the 50ft run on the inside does this make it better? What do you guys suggest? Thanks

Thank you for reporting this comment. Undo
Chriss123

Or should I just make a 8/3 100ft cord? I know its expensive, but I want it done right and safe.

    Bookmark   December 9, 2012 at 3:35PM
Thank you for reporting this comment. Undo
Ron Natalie

You can make a cord. Note that cordage counts the ground so you need 8-4 (unlike cable which doesn't count the ground).

You can't run cord through the walls/structure, so unless the transfer switch is mounted exterior (or in the garage or someplace you can go through the door), you'll need to mount a inlet on the house and run approved interior wiring to the transfer unit.

    Bookmark   December 10, 2012 at 9:07AM
Thank you for reporting this comment. Undo
Chriss123

Can I get away with 8/4 on the inside from the transfer switch to the inlet box and just do the rest (50ft) with a pre made cable of 10/4? Would this help with voltage drop vs doing everything in 10/4. Thanks

    Bookmark   December 10, 2012 at 4:54PM
Thank you for reporting this comment. Undo
Ron Natalie

I think you mean 8/3. Cables don't count the ground again (cords do).

Yes, you can use cable inside the house (provided it is rated for interior use, I'm assuming you're talking about something like NM). Going up a wire size when you've got high currents over longer runs isn't a bad idea.

    Bookmark   December 11, 2012 at 9:24AM
Thank you for reporting this comment. Undo
Chriss123

Your correct 8/3. I'm going to just make a straight 85-100 ft cable and run it directly from the gen to the transfer switch.

    Bookmark   December 11, 2012 at 8:25PM
Sign Up to comment
More Discussions
Can I electrify battery-operated lights?
Hi all. Is there a way to electrify a battery operated...
eam44
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Two fans on same circuit in different rooms, can't get wiring right
So here's the situation. I have two ceiling fan/lights...
jenfarino
Sponsored Products
Bali Exterior Solar Shades: Shoji (10% Openness)
Blindsgalore
5" Fluorescent IC Housing by Juno
$51.46 | Lumens
Slumber Solutions Choose Your Comfort 8-inch Queen-size Memory Foam Mattress
Overstock.com
Cypress Folding Beach Chair
Fifthroom.com
All-weather Number Art #6
Grandin Road
Green & White Sleek Scrape Collapsible Scraper
$11.99 | zulily
White Butterfly Garden Small Bowl
$46.00 | Horchow
Ace Bayou 4.1 Pro Series X-Rocker Pedestal Wireless Game Chair - 5129601
$189.98 | Hayneedle
© 2015 Houzz Inc. Houzz® The new way to design your home™