grounding means to branch panel

uniflowDecember 5, 2012

Greetings, I am upgrading a 100A QO remote panel in a detached building from 120V to 240V with 2-4 Al cable (all that was available locally) pulled from a 200A QO entrance panel. I gutted the remote panel and removed the bonding screw and installed a box grounding bar, drove an 8" ground rod and cabled it to the bar along with all the branch circuit grounds, separating them from the neutrals.

I have two questions: This leaves me with the insulated green conductor. May I ground it at the entrance panel as well as the remote panel? A journeyman electrician said that I could do this but I want a second opinion.

The other is, there is not available in either panel a means to ground the large #2 wire. May I bolt a grounding lug inside each panel case and install the grounding conductor to them?
Thanks for your help! Jim

Thank you for reporting this comment. Undo
Ron Natalie

The current codes require that you run a ground to the remote structure in addition to it having it's own grounding system.

What green conductor are you talking about? Are you talking about the one feeding the sub panel? In this case not only CAN you, you MUST connect that to the grounding system on both ends.

You can use listed accessory lugs, check the Schneider catalog.

    Bookmark   December 5, 2012 at 10:02PM
Sign Up to comment
More Discussions
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™