Unusual GFCI Breaker

djdoggoneDecember 11, 2012

We have an unusual GFCI breaker and are wondering if it is special in some way. It has two white wires coming out of it: one curly with a black line down the side and the other a straight white wire about 2 ft. long. It is a Siemens/ITE/Gould CAT# OF-115.

All the GFCI breakers we see have just the one curly wire.

Any hints?

Thanks, Deb

Thank you for reporting this comment. Undo
brickeyee

Is there a neutral screw on the breaker along with a hot screw?

One of the whites is likely neutral out to the load, while the other is neutral for the bar in the box (neutral into the GFCI and out of the GFCI).

    Bookmark   December 11, 2012 at 3:47PM
Thank you for reporting this comment. Undo
weedmeister

Something like this?

Here is a link that might be useful: Seimens QF115 breaker

    Bookmark   December 11, 2012 at 4:10PM
Thank you for reporting this comment. Undo
djdoggone

brickeyee: no neutral screw. know curly q goes to neutral bar on box. second white wire, about 6 inches long, think gets twisted with white wire from circuit. just want to be sure.

weedmeister: you got it! am i right in how to wire?

    Bookmark   December 11, 2012 at 4:44PM
Thank you for reporting this comment. Undo
Ron Natalie

Brick nailed it. The coily wire goes to the neutral bus. The straight one gets wirenutted to the load neutral.

    Bookmark   December 11, 2012 at 7:22PM
Thank you for reporting this comment. Undo
djdoggone

Can't thank you guys enough.

    Bookmark   December 12, 2012 at 10:52AM
Thank you for reporting this comment. Undo
brickeyee

Just so you understand, both the hot and neutral of the load must pass through a GFCI device.
It is measuring if the currents in these lines match (within about 0.006 A (6 mA).

Any mismatch is taken to be caused by a problem, and the device turns off the circuit.

Many GFCI breakers have a terminal for mounting the branch circuit neutral, and a wire for then hooking up to the panel neutral buss.

This one just uses wires for both connections.

    Bookmark   December 12, 2012 at 1:13PM
Sign Up to comment
More Discussions
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Wiring Ceiling fan
I have a new ceiling fan with a light. The fan has...
jjp2121
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
© 2015 Houzz Inc. Houzz® The new way to design your home™