grounding electrode

JasmarDecember 31, 2013

Getting all my ducks in a row for a meter/main panel(disconnect) replacement, have spoken to POCO and local inspector and have confirmed that they do not want any grounding/bonding in the meter can and that they want pvc used between the meter can and the main panel. City requires that the cold water pipe be used as the grounding electrode when house has copper piping even though its plastic from the water company to the meter in the yard. They require one ground rod to be used as additional grounding electrode. Water comes in on the opposite side of the house from where the electrical comes in. Any reason I could not land the cold water GEC on the ground lug in the main and the land the GEC for the ground rod in the bottom of the panel on the ground/neutral bar or is there a reason they should be bonded outside of the panel itself? Could I bond the ground rod to the copper plumbing somewhere other than where the primary GEC is connected to the cold water line (where it enters the house)?
Which would be the best option (are any non code compliant)?
#4 between main panel and cold water pipe then using separate clamp on same cold water line, #6 through wall to ground rod.
#4 between main panel and cold water pipe landed on ground lug at top of panel, #6 connected to ground/neutral bar and run through bottom of panel and outside wall to ground rod.
#4 between main panel and cold water pipe then #6 bond between copper pipe and ground rod on opposite side of house (about 25 foot from where cold water line enters house)
J

Thank you for reporting this comment. Undo
Ron Natalie

Your supplemental electrode can be connected to the panel (provided the terminal is up listed for the conductor size in question).

You're not required to go over #6 cu on the connection to the supplemental electrode, you could if you wanted to.

I'm surprised the inspector will permit only one supplemental rod electrode. The NEC rule is that the supplemental electrode needs to meet the same rule as if it were the sole electrode (which usually requires two rods).

    Bookmark   December 31, 2013 at 8:12AM
Thank you for reporting this comment. Undo
bus_driver

To borrow from another saying, the inspector ain't always right but he is always the inspector.
I had one stubborn inspector who had not even bothered to look at the job but refused to pass it. So I knew another electrician who was personal friends with the inspector. That electrician came and looked and found all to be OK. So I hired him to be the electrician of record and the job passed with no changes.
No wonder that I am wary of authority.

    Bookmark   December 31, 2013 at 9:56AM
Sign Up to comment
More Discussions
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™