Too Many Amps?

Pooh BearNovember 19, 2006

This is a direct quote of something in the

December issue of Popular Mechanics.

What do y'all think of their answer.

I saw this and was curious about it.

Pooh Bear

----------------------------

Too Many Amps?

My 200-amp electrical panel box has 400 amps' worth of circuit breakers. Is this safe?

Yes. It's better to have many individual circuits than fewer circuits with larger electrical loads. Also, not every circuit will be energized at the same time, and it's unlikely that they will see the full load for which they are rated.

For example, a 120-volt, 15-amp branch circuit that provides power to four lighting fixtures, each of which has a 150-watt bulb, uses only 5 amps.

Thank you for reporting this comment. Undo
normel

Sounds good to me.

    Bookmark   November 19, 2006 at 10:08PM
Thank you for reporting this comment. Undo
petey_racer

Yup, dead on except for one fact. He says not all circuits will be "energized". I think he meant to say "will not have a load", or current applied. Perhaps he was simply "dumbing it down" to a lay person's level.
No offense meant to any lay persons.

    Bookmark   November 19, 2006 at 11:07PM
Thank you for reporting this comment. Undo
Ron Natalie

...or loaded up to the breaker capacity.

    Bookmark   November 20, 2006 at 10:38AM
Thank you for reporting this comment. Undo
normel

"Energized" sounded good to me, but then I was watching a Star Trek marathon at the time...the old ones are still the best and I remember them from their first run.

    Bookmark   November 20, 2006 at 11:18AM
Thank you for reporting this comment. Undo
Pooh Bear

Ok, I was just curious.

I remember a discussion from last year about amps of service
and from what I read you have two wires coming in from the pole
and for 200 amp service each line is capable of 200 amps.
Making the breaker box capable of 400 amps worth of breakers.
Is this relevant to this post in any way.
Such that what if instead of 400 amps worth of breakers,
It was 200 amp service with 500 amps worth of breakers.

Just curious is all.

Thanks.

Pooh Bear

    Bookmark   November 20, 2006 at 7:59PM
Thank you for reporting this comment. Undo
petey_racer

No, not relevant or accurate. Sorry.

    Bookmark   November 20, 2006 at 9:08PM
Thank you for reporting this comment. Undo
Pooh Bear

Not accurate? Could you elaborate?

It was a post on this forum and the general consensus was
that each line from the pole was able to provide 200 amps.
That was my understanding. (but I got fluff for brains).

Pooh Bear

    Bookmark   November 20, 2006 at 10:48PM
Thank you for reporting this comment. Undo
petey_racer

Yes, a 200 amp service is capable of delivering 200 amps per leg.
A 200 amp residential service is 200 amps at 240v. Or the equivalent of 400 amps @ 120v.
More precisely 48,000 watts worth of power.

This is NOT a "breaker box capable of 400 amps worth of breakers."
The sum of the breaker is of NO consequence. It is not uncommon to have 600-800 amps worth of breakers in a 200 amp panel.

    Bookmark   November 20, 2006 at 11:20PM
Thank you for reporting this comment. Undo
Pooh Bear

Wow, interesting info.
I really didn't know any of this.
It does make more sense to me now, tho.

In the house I grew up in we had an electric heat pump, electric water heater, electric kitchen stove, electric clothes dryer, and I had several 220 outlets in a workshop. Now I don't know exactly what all those pull in amps but I would guess it pushes the 200 amp limit. And then add in all the 110v loads. And it's not inconceivable that all that could have been running at the same time. It's an interesting thought to ponder. (to me anyway).

Thanks for explaining it.

Pooh Bear

    Bookmark   November 21, 2006 at 12:49AM
Sign Up to comment
More Discussions
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Disposer Power Cord
I recently bought a GE disposal online. The model is...
africanboy
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Sponsored Products
71" Carignan Stainless Steel Footed Tub
Signature Hardware
Florence Style Loft Leather Loveseat in Black
$749.00 | LexMod
Jett Adjustable Floor Lamp
Overstock.com
Campania International Pisa Cast Stone Bird Bath - B-054-AL
$109.99 | Hayneedle
Santa & Cole | GT5 Pendant Light
$790.00 | YLighting
Homelegance McKean Extension Dining Table in Black & Brown
Beyond Stores
Bronze Three-Light Billiard Pendant with Raspberry Crystal Glass
$510.40 | Bellacor
Bourgie Table Lamp
Design Within Reach
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™