Laundry Room Washer on Dedicated Circuit?

Tom PultzNovember 12, 2009

Our laundry room has two 120V receptacles, one for the washer and another one on the opposite wall on the same circuit. Both are non GFCI. We are installing a laundry sink, cabinets and countertop next to the W&D on the same wall and would like to have another receptacle on that side of the room also.

Can we tap into the existing circuit to add the extra receptacle? I was under the impression that the washer was supposed to be on its own dedicated (GFCI?) circuit.

Thanks for any input.

Thank you for reporting this comment. Undo
hexus

yes you can do that as it will in the same laundry room.
You only are going to need to GFI them if they're 6 feet or less from the outer edge of the sink.

    Bookmark   November 12, 2009 at 6:55PM
Thank you for reporting this comment. Undo
bus_driver

A washing machine does not have to be on a GFCI. In fact, the washer might cause nuisance tripping of the GFCI. Yes, you can add receptacles in the laundry room from the existing circuit. And it might be wise to cease accepting electrical wiring advice from your previous sources.

    Bookmark   November 12, 2009 at 6:56PM
Thank you for reporting this comment. Undo
hexus

"And it might be wise to cease accepting electrical wiring advice from your previous sources."

that made me laugh, however for some reason GFI protecting the washer receptacle seems to be something people struggle with. I have one state inspector in one area I do work in that insists that we have to GFI it. I've tried arguing and finally decided it's not worth it and always just have to remember to throw in an extra GFI on the trim.

    Bookmark   November 12, 2009 at 7:01PM
Thank you for reporting this comment. Undo
Tom Pultz

Well, what if the washer receptacle is less than 6 ft from the sink? Is it still "exempt?" Maybe I should switch that from a duplex to a single receptacle.

When we add the laundry sink then the current extra receptacle and any others we add will need to be GFI protected because they will be within just a few feet of the sink.

Thanks for clearing up my question whether the washer needed a dedicated circuit. I thought I read that in this forum, but it was probably that the laundry room needed to be on a dedicated circuit.

    Bookmark   November 12, 2009 at 7:30PM
Thank you for reporting this comment. Undo
petey_racer

Hexus IS right, under the 2008 NEC.

Any exceptions to the GFI rules for laundry rooms and basements have been removed.
If it is within 6' of a laundry sink it MUST be GFI protected. Period.
Appliances are much less likely to nuisance trip these days, and GFI's are getting smarter and less touchy. So the whole nuisance tripping thing is becoming less of an issue.

Tom, the "laundry" needs a circuit, not the washer alone. As the others said, you CAN add a receptacle to this "laundry circuit".

    Bookmark   November 12, 2009 at 7:37PM
Sign Up to comment
More Discussions
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™