Subpanel question

ylmzmNovember 14, 2013

I need to put a subpanel on the external wall of the house (far end of the house) for feeding many outdoor receptacle circuits for the backyard.

I will initially use it for six 20 Amp circuits. These circuits are very unlikely to be used all at once. I will probably need couple of more circuits in the future.

I think all I need is a 60 Amp rated panel, but I need a lot of circuit spaces. I cannot find a low Amp rated panel with many spaces. It looks like I need to buy a 125 Amp rated one to be able to get a lot of circuit spaces. This is all fine, but the question is the following:

The subpanel will be driven by a 60 Amp double pole breaker. Can I use #6 wires to a 125 Amp rated panel in this case?

Thank you for reporting this comment. Undo
Ron Natalie

As long as the panel is rated as big or larger than the feeder, it is OK. You can treat the 125A panel as if it were a 60A one.

    Bookmark   November 14, 2013 at 7:42PM
Thank you for reporting this comment. Undo
btharmy

If the receptacles will not be used at the same time, why do you think they all need to be on dedicated circuits? How big are the connected loads going to be?

    Bookmark   November 14, 2013 at 9:46PM
Sign Up to comment
More Discussions
Ceiling fan wiring
I have a new ceiling fan with a light. The fan has...
jjp2121
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
© 2015 Houzz Inc. Houzz® The new way to design your home™