Generator Hookup

tomdxNovember 10, 2012

My (7250/8250) generator has 4 outlets. Two GFI's, 1 L5-30R, 1 L14-30R. During the recent storm I used the GFI outlets and everything worked fine... but I've been told I should use one of the 'L' outlets to properly balance the load.

So I have a couple of questions...

- What's the difference between the two?

- Which one should I get a cord for?

(I'd be connecting to regular 12g extension cords)

- Are the outlets mutually exclusive?

(ie, if I use the L-14 is the GFI or LS available for use)

Thanks

Tom

Thank you for reporting this comment. Undo
Ron Natalie

The GFIs as well as the L5-30R are all hooked to the same side of the generator. There's nothing that you will accomplish plugging things in there that will get you more than the aggregate 30A the main breaker will allow.

The L14-30R will allow you to put ~30A 120V loads on both 120 legs of the generator getting closer t he rated power of the generator.

You can use all the receptacles together. The 120V receptacles are protected by their respective push button circuit breakers and then they run into one side of the main 30A breaker.

    Bookmark   November 11, 2012 at 6:19AM
Sign Up to comment
More Discussions
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™