First perhaps a stupid question. I have a 200 amp breaker box but if I add up the breakers, it comes to near 800 amps. Is the thought that while I have 200 amp service, it is unlikely I would ever be drawing full current through even 25 % of them?

A couple of years ago a electrician installed split breakers in about 40% of the slots in my main breaker box to handle extra outlets I wanted throughout the house. We are about to undergo a kitchen remodel that includes a second electric oven but little more power required. The contractor was making noises that he thought a new main box might be needed. It didn't seem that the oven was the problem but that we would have more dedicated circuits needed to bring to current code. So why can't more of the regular breakers be split to get the extra lines? There are still plenty of 15 and 20 amp breakers that could be split. Is there a limit on split breakers to a box?

Thank you for reporting this comment. Undo
mike_kaiser_gw

I want to say the limit is 42 but that may depend on what version of the code your municipality is using. The manufacturer of the panel will also limit the number of circuits. Check the label for the number.

The combined amperage of the individual breaker will always (or almost always) exceed that of the main breaker. You typically don't use everything at once but there are calculations you or your electrician can perform to see if you have a large enough service.

    Bookmark   November 14, 2009 at 2:39PM
Thank you for reporting this comment. Undo
Ron Natalie

The limit is what the panel supports. It used to be code to limit the maximum OCD's to 42. Some panels accepted less. Some only accept tandems in certain slots to prevent you from exceeding the old 42 limit. It should be marked on the panel somewhere.

    Bookmark   November 14, 2009 at 6:29PM
Thank you for reporting this comment. Undo
azlighting

The sum of your breakers can be more than the service size, which is ok. Load capacity can only be %80 of the circuit breaker size. The only thing you need to worry about is the actual load. This cannot be more than your service size, which may be what your electrician is talking about. He may think you are getting close to the service size.
Do a load service calculation to determine what the actual load is.

    Bookmark   November 15, 2009 at 1:29AM
Thank you for reporting this comment. Undo
mikie_gw

i used to think of it as 10a per pole per amp of main
150 a main 1phase 30 poles max
200 a main ditto 40 poles max
100 a main 20 poles max

    Bookmark   November 16, 2009 at 3:20AM
Thank you for reporting this comment. Undo
brickeyee

"i used to think of it as 10a per pole per amp of main"

No such requirement exists.

    Bookmark   November 16, 2009 at 8:53AM
Sign Up to comment
More Discussions
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Sponsored Products
Tech Lighting | 12V 300W Single-Feed Surface-Mounted Magnetic Transformer for TE
$445.60 | YLighting
Dramm Syphonject Siphon Mixer - 1403-1041
$29.99 | Hayneedle
Tech Lighting | Two-Circuit Remote Transformer - Magnetic -Single Feed -12V 600w
$576.80 | YLighting
DuroStar 10,000-Watt 16.0 Hp Gas Generator with Electric Start Kit
Overstock.com
Dramm Aluminum Quick Disconnect - 1403-1116
$30.99 | Hayneedle
Tech Lighting | 24V 300W Single-Feed Surface-Mounted Magnetic Transformer for TE
$457.60 | YLighting
Tech Lighting | 24V 300W Electronic Single-Feed Surface Transformer Wall MonoRai
$445.60 | YLighting
Le Salon Matt Breaker 10 blades - 91244
$14.99 | Hayneedle
© 2015 Houzz Inc. Houzz® The new way to design your home™