Flip the switch and breaker trips, cause is?

stash-hdyNovember 2, 2008

When the attic light switch is flipped to on, the breaker trips. Under this condition is it correct to assume that the problem lies at the swich or between the switch and the light. In the switch off position the circuit if fine.

Thank you for reporting this comment. Undo
bigbird_1

The short to ground could be anywhere in the circuit. As soon as you close the switch, unlimited current is flowing in the circuit. The only place unlimited current can flow to is to neutral/ground. The unlimited current trips the breaker. The problem is most likely at the switch or light. However, a nail through the cable at any point or a rodent chewing through the cable jacket could also cause this problem.

    Bookmark   November 2, 2008 at 9:45AM
Thank you for reporting this comment. Undo
stash-hdy

How would you find the short to ground if its not in the attic switch circuit? Not knowing the wiring within the walls? Could it be in a plug on the opposite wall, would they have ran the light from a plug? The breaker is labeled kitchen lights, if I flip the breaker, find all the lights and plugs on the circuit and check each?? Help

If it's a nail does the wire need to be replaced?

    Bookmark   November 2, 2008 at 10:07AM
Thank you for reporting this comment. Undo
bigbird_1

Usually in a case like yours with a dead short, a wire has come loose at a switch or device and is shorting out the hot wire. I'd start troubleshooting by visually checking all wires at every switch and device in the circuit controlled by the breaker (kitchen lights) which is tripping. Make sure the wires are connected to where they are supposed to be. If no one has been doing any remodelling or picture hanging then there isn't much reason to suspect a nail or screw has suddenly punctured a wire. Also check any GFCI receptacles on the circuit for malfunction. If you have a nail or screw puncture, which is unlikely, you can replace the cable around the fault by using junction boxes for the splice.

    Bookmark   November 2, 2008 at 10:33AM
Thank you for reporting this comment. Undo
petey_racer

How would a nail find a wire? Did you go around nailing things to the walls?

Shorts are RARELY along the wiring within the walls. Usually they are at a box or other outlet.

How did this come about? Did it just start happening? Were you messing around with anything?
Details, we need details!

    Bookmark   November 2, 2008 at 11:46AM
Thank you for reporting this comment. Undo
bigbird_1

The OP never stated that he/she was nailing anything to the walls. I stated that it was very unlikely for this to happen. I suggested that the OP check every switch and device for correct wiring with no shorts to neutral/ground.

    Bookmark   November 2, 2008 at 12:06PM
Thank you for reporting this comment. Undo
shadetree_bob

Agree with petey, unless you have been nailing something to the wall or ceiling, nails are not likely to be involved. I have experienced HOT NAILS. They went thru one wire and did not cause any breaker poppage. When you touched the nail it was quite a thrill though.

I would start by taking the switch plate off, (NOT the switch) and with a handy flashlight inspect for any wire touching the side of the box or other wires. Then if you seen nothing out of the ordinary replace the plate and flip the switch or manually flip the breaker. Is the light just a light or is it a ceiling fan? Fans can vibrate connections loose and cause this problem. If you know how, remove the cover and look in the ceiling box, With the info you have given you should find the problem in one of these two places. If this is getting into unfamiliar territory for you, CALL AN ELECTRICIAN, , it's not worth the shocks you could receive, just to save a few bucks!!

    Bookmark   November 2, 2008 at 12:35PM
Thank you for reporting this comment. Undo
normel

When the attic light switch is flipped to on, the breaker trips. Under this condition is it correct to assume that the problem lies at the swich or between the switch and the light. In the switch off position the circuit if fine.

The problem will be at the switch or the light, or to a lesser possibility in the wire between. There should be no need to check all the devices on the circuit.

    Bookmark   November 2, 2008 at 12:42PM
Thank you for reporting this comment. Undo
petey_racer

Sorry BB, I thought I read that the OP suggested that. My fault for reading too fast.

    Bookmark   November 2, 2008 at 2:46PM
Thank you for reporting this comment. Undo
joed

A case like this is usually the result of a switch loop being mis wired. You are actually turning the switch on when the breaker trips.
Did you do any changes to the wiring at the light? Did you decide it was mis wired because all the colours didn't match?

    Bookmark   November 2, 2008 at 7:37PM
Thank you for reporting this comment. Undo
stash-hdy

The problem was the wire, switch and light OK. It was not worked on since the house was built, something shorted out the wire. I could not get the original wire out of the wall, clipped the ends and left it. Thanks for the help in resolving the problem.

    Bookmark   November 6, 2008 at 9:50PM
Sign Up to comment
More Discussions
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Sponsored Products
Battery Operated Red Glitter Candles - 4"H
Grandin Road
Casdon Kids Play Electronic Microwave - 492
$37.99 | Hayneedle
Robert Sonneman Perch Polished Chrome Desk Lamp
Euro Style Lighting
George Kovacs | Circuit Mini Pendant Light
$130.00 | YLighting
Hughes Leather Sectional with Bumper (2 piece) - Brighton Zinc Beige
Joybird Furniture
Natural Light All Wrapped Up Floor Lamp With Linen Shade
Lamps Plus
Rite Lite 6-LED Gold Wireless Picture Light LPL602G
$15.97 | Home Depot
Waring Pro Toaster Oven and Toaster
$99.50 | FRONTGATE
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™