Junction Box vs Subpanel

dyi_calNovember 27, 2006

I am running 220v service from a 200 amp metered load center on a power pole 220 feet to a 100 amp Manufactured home pad. I will be using 3 wires ( ok per local building code but need to ground at the pad). I will be running underground thru PVC conduit. My questions is can I terminate the feed in a junction box (supported by a post) at the pad or do I need a subpanel. If I use a subpanel, the will be 3 100amp breakers used (main panel, subpanel and Manufactured home panel). If I use a junction box, the installer can go from the junction box to the Manufactured home panel. Thanks for your advice.

Thank you for reporting this comment. Undo
kurto

I'm just a DIYer, but I would put a disconnect on the pole at the pad, rather than a sub-panel or just a plain junction box. If nothing else, it would give you a place to connect your two ground rods.

I'm sure one of the real electricians will comment.

    Bookmark   November 27, 2006 at 12:35PM
Thank you for reporting this comment. Undo
brickeyee

If there is a disconnect at eh pole it need overcurrent protection. Just a switch is not acceptable.
Every panel after the pole is a sub-panel.
You need to run 4 wires to the various sub-panels.
The 'farmer disconnect' of a switch with no overcurrent protection may be acceptable in your area, but the number of these ares continues to shrink.

    Bookmark   November 27, 2006 at 10:00PM
Thank you for reporting this comment. Undo
dyi_cal

Just thought I would document how this wiring job ended up. Used 4" conduit from main pole to subpanel on post within 5 ft of Manufactured home. 125a breaker in main box and 100a in subpanel. Pulled 4 wires - (3) 1/0 THHN for power and neutral and (1) #4 THHN for ground. The manufactured home setup crew then wired from the 100a breaker in the subpanel to the 100a panel on the manufactured home. All systems function fine with no noticable voltage drop. I had to add a grounding bar in the subpanel and measured to assure there was no path between ground and neutral in the box.

    Bookmark   April 7, 2007 at 10:36PM
Thank you for reporting this comment. Undo
coolvt

The NEC has special provisions for mobile homes. By code you had a to have disconnecing means within either 25' or 35' of the home (can't remember which). So that part is correct.
Myself and other mobile home park owners had a real battle with our State chief inspector and the department's legal force. They insisted that we could not put disconnects at the power pole (which included the meter). It seemed kind of stupid to us because then the wire from the pole to the disconnect outside the home had no overcurrent protection, but they insisted this was their interpretation of the code.
You might know it, the first park that we call for an inspection on, the local POCO refuses to energize without disconnects at the meter. They claimed that they had jurisdiction and they wanted the disconnects. As far as I know, none ever got done without the disconnect at the pole/meter regarlsess of what the State wanted.

    Bookmark   April 7, 2007 at 11:12PM
Thank you for reporting this comment. Undo
dyi_cal

Interesting issue. Glad nothing like this came up with me. The owner of my electrical supply house is a licensed electriction and has an active business. He advised me on this also as did this forum. I also called the Manufactured home set up crew owner and discussed it with him. SLO county inspection was very happy with the installation as was the setup crew. Thanks for you input.

    Bookmark   April 8, 2007 at 2:28AM
Sign Up to comment
More Discussions
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™