bathroom light switch located too close to shower

blindmanbruceNovember 11, 2010

Planning to Renovate my bathroom:

According to what research I've done, there cannot be an electrical switch within "X" amount of inches from a tub or shower. (I think it is sixty something inches, can't recall exactly). However, my problem is that the current location of the switch box as you enter the bathroom is around 24" from the shower stall. It's right along the edge of the bathroom entry door so it cannot be moved over any further.

Moving it would require installing a new door that would open opposite and also moving the switch to a new location on another wall. This would cause the door to open into and hit the base of the shower stall and would be create a somewhat awkward entry into the room. (The bathroom is on the second floor so moving the shower would require me to also move the toilet etc... which would lead to re-plumbing the entire bathroom among other things and is out of the question.)

Are there any exceptions or conditions where a light switch can be in close proximity to the tub or shower? What are my options?

Thank you for reporting this comment. Undo
Ron Natalie

My entire bathroom isn't 60 inches long. There's no prohibition on switch location as long as it is not INSIDE the shower area.

    Bookmark   November 11, 2010 at 7:50AM
Thank you for reporting this comment. Undo
blindmanbruce

Thanks for the clarification ronnatalie.
I always read too much into things. I figured that a switch or outlet would not be installed inside the shower/tub area (it's just common sense); I forget that the code has to sometimes state the obvious for people who have no common sense. In cases where the obvious is stated I start looking for a more complicated reason. My thought was that they didn't want you to be standing in water and be within "reach" of anything electrical. For light switches I guess I can understand it, ie. if you were in the shower you would have little reason to use the switch. You certainly wouldn't want to turn off the light while you're in the shower.
But what about a switch for an exhaust fan or a switch for a light that is over the shower? Is there any restriction on those? Is it the same for gfic outlets as well?

    Bookmark   November 11, 2010 at 12:17PM
Thank you for reporting this comment. Undo
hendricus

I figured that a switch or outlet would not be installed inside the shower/tub area

The house we moved into 6 yrs ago, built in the 1950's, had the switch in the tub/shower. Originally it had the tub, then the whole bathroom was tiled and a shower added to the tub. Now the switch was in with the shower. It was pretty safe though, the shower was on one end and the switch on the other. Never got real wet.

    Bookmark   November 11, 2010 at 3:27PM
Thank you for reporting this comment. Undo
alan_s_thefirst

You could always put the switch outside the bathroom...

    Bookmark   November 16, 2010 at 12:45AM
Thank you for reporting this comment. Undo
stash-hdy

Find out your local code and what the actual nation code is? Your local code will apply along with the national code when you get a permit and itâÂÂs inspected. You also want to be safe in the shower. Switch within the shower!!!!!!!!!

    Bookmark   November 16, 2010 at 8:11AM
Thank you for reporting this comment. Undo
Ron Natalie

New construction in NJ is governed by the 2008 NEC, rehab work may be allowed to comply with the 2005 code alone. As I stated, either version of the NEC only specifies that the switch be OUTSIDE the shower area. There's no minimum distance.

    Bookmark   November 16, 2010 at 8:19AM
Thank you for reporting this comment. Undo
pdurham_gmail_com

Per the 2008 NEC:

Article 404 "Switches", Part 4 "Damp or Wet Locations":
Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

Article 406 "Receptacles", Part 8 "Receptacles in Damp Locations":
(C) Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall.

(Note: A "receptacle" is defined as an outlet where a user connects a plug.)

Article 410 "Luminaires, Lampholders & Lamps", Part 10 "Luminaires in Specific Locations":
(D) Bathtub and Shower Areas. No parts of cord-connected luminaires, chain-, cable-, or cord-suspended luminaires, lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the space directly over the tub or shower stall. Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray.

Hope this clarifies.
-Patrick

    Bookmark   March 5, 2011 at 3:54PM
Thank you for reporting this comment. Undo
texasredhead

Alan has the best idea. One of our bathrooms where it would be an issue, the light switch is on the outside wall entrance to the bathroom. If you are really concerned, simply cut a hole for the box and turn the switch around to face the wall entering the bathroom. Mine has a lighted dimmer switch. Inside the bathroom on the wall opposite from the tub/shower is a switch to control the ceiling fan and a GFCI switch for hair dryers and the like.

    Bookmark   March 6, 2011 at 9:03AM
Thank you for reporting this comment. Undo
texasredhead

I meant a GFCI receptacle.

    Bookmark   March 7, 2011 at 7:52AM
Sign Up to comment
More Discussions
Swimming pool wiring
I have 2 gfci circuits operating two pool pumps. Is...
dalemd88
can homeowner so electrical work in his own home ? (above ground pool)
I live in Western ma and I'm having an Adobe ground...
growingadvice
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
© 2015 Houzz Inc. Houzz® The new way to design your home™