Have someone suing me and they have a newly lisenced GC who claims that having a mian breaker in the sub panel is against code - can anyone tell me if this is true and if not the california code that I can use to say its not

Thank you for reporting this comment. Undo
ms01634

in NJ I installed a sub panel and it was definitely wrong to have a main breaker in it. The main breaker is the breaker in the main panel that is feeding the subpanel. Its redundant anyway if you think about it. The sub panel had a groung and a nuetral that BOTH go to the main panel ground.

    Bookmark   October 9, 2010 at 8:28PM
Thank you for reporting this comment. Undo
mike_kaiser_gw

I think your first call should be to your local building department. They're the final authority as to what is acceptable and what is not.

Who installed this sub-panel? Was it inspected? If so, that should cover you.

    Bookmark   October 9, 2010 at 9:14PM
Thank you for reporting this comment. Undo
terribletom

Using a load center equiped with a main breaker for a sub-panel is done all the time and there is nothing wrong with it per se. The "main breaker" in the sub-panel becomes nothing more (or less) than a local disconnect for the sub-panel.

My hunch is that either (1) the 'GC' (who, btw, is probably not a qualified expert for the purposes of court testimony on electrical matters) doesn't know what s/he is talking about or (2) the alleged code violation is something other than what you've described.

Off the top of my head, here are a couple of possibilities you might want to consider:

The local sub-panel disconnect (i.e., second "main breaker") does nothing to protect the feeder wires from the main panel to the subpanel. Thus, if you wired the feeders from the main panel lugs (as opposed to a properly sized breaker), the feeders are exposed to the total current of the main service and may be undersized.

For example, assume the house has 200A service and you wired a 100A subpanel using #2AWG wire connected to the main lugs. While #2AWG is adequate for the 100A subpanel, it is not adequate for the 200A supplied to the main lug and this would be a code violation.

What size feeder conducters were used and are they properly protected by a breaker in the main panel? Assuming that they're connected to a breaker, it is THAT breaker that is the important overcurrent device and the primary disconnect for the sub-panel.

Secondly, it's possible that you interpreted the fact that the sub-panel had a "main breaker" and was marked suitable for use as service equipment" as meaning that it should be wired like a main panel -- specifically that the neutrals and grounds can be co-mingled as is legal in a main panel. Does the sub-panel have a ground bar and are the neutrals and equipment grounds kept isolated? If not, then you have a code violation.

Finally, it's possible that the "GC" is the one doing the misinterpreting. That is, perhaps s/he decided (incorrectly) that since it was a "main panel" the neutrals and grounds should be bonded.

Who knows? You need more facts.

    Bookmark   October 10, 2010 at 8:22AM
Thank you for reporting this comment. Undo
brickeyee

"in NJ I installed a sub panel and it was definitely wrong to have a main breaker in it."

They must have changed the local code since the NEC does not prohibit a main disconnect in a sub-panel.

It is not required, but does make working tin the box at least a little safer.

You can turn off the 'main' in the panel and know that the breaker lugs are no longer hot.

Only the panel feed and the source side of the 'main' remain hot.

    Bookmark   October 10, 2010 at 12:40PM
Thank you for reporting this comment. Undo
smithy123

A main breaker in a subpanel is POINTLESS unless it is smaller than the feeder breaker. if it is the same size or larger then it decomes a ''line of sight disconnect'' (joke)

    Bookmark   October 13, 2010 at 9:54PM
Thank you for reporting this comment. Undo
ontariojer

A larger main breaker in a sub-panel may be pointless, but it is frequently cheaper to use it than a panel without. Like HALF the cost sometimes. Supply and demand I guess. Kind of like spa- paks vs. Tandem GFI breakers.

    Bookmark   October 13, 2010 at 10:38PM
Thank you for reporting this comment. Undo
DavidR

OJ has it right. Often you can get package deals in one carton, with a main panel and several breakers, for less than you'd pay for a main lugs panel alone. I guess it's because they're produced in large quantities for builders and the competition is strong.

A main breaker in a sub is no big deal aye or nay, if the sub is right next to the main panel. But if it's on the other side of the house, or on a different floor, that local disconnect is nice to have.

    Bookmark   October 15, 2010 at 2:17PM
Sign Up to comment
More Discussions
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Oil in Motor of Ironrite Rotary Iron. what do I do now?
Hi, I just bought an old 1946 Ironrite rotary iron...
lucinda002
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
Sponsored Products
Los Feliz Small Outdoor Wall Mount
$430.00 | Bellacor
Clarity II Ceiling Fan by Monte Carlo Fans
$349.00 | Lumens
Creme Bell Shade Brushed Nickel Swing Arm Desk Lamp
Lamps Plus
Established & Sons | Cape Sofa
YLiving.com
Cole & Co. 36" Designer Series Collection Canterbury Sink Chest - Parchment
Modern Bathroom
Stirrup 3 Uplighter/ Floor Lamp
Design Within Reach
Alamere Rainfall Nozzle Shower Head with S-Type Arm
Signature Hardware
Floral Pendant - Black - David Trubridge
$630.00 | HORNE
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™