Little Generator, Big Inlet

john2175October 3, 2011

My house has a properly wired (I assume) NEMA 30 amp-120/240 Volt generator inlet receptacle (l14-30) which was designed to handle say a 4000 Watt generator.

However I only own a 2000 Watt-120 Volt generator that has two NEMA 20 amp/120 Volt outlets (5-20).

Can I safely make a conversion cord to hook one of these outlets to the inlet receptacle and power both electrical bus bars at the main ciruit breaker panel?

I know that only 120 Volts are available so I will just have to keep all of the 240 Volt circuits switched off.

I also know that I have 16.7 amps max and will have to carefully manage which 120 Volt circuits I switch on.

The main circuit breaker panel has the necessary interlock switch (this is why I assume that the whole generator inlet circuit has been properly wired).

I'd rather not buy a bigger generator until I see if I can live with the smaller one.

I'd rather not rewire the existing generator circuit.

Thank you for reporting this comment. Undo
Ron Natalie

Well, it's not Kosher but it's probably OK. 240 won't work (you'll see zero volts there and if they have a neutral connection as well who knows what they might do). You'd have a problem with multiwire branch circuits as well as you could put twice the load on the neutral as it may see in normal use, but given the fact the generate is going to keel over at 17A, it's hard to imagine you'll overload it that much.

    Bookmark   October 3, 2011 at 4:47PM
Thank you for reporting this comment. Undo
sswillow

I'm thinking of doing this, also, for my EU2000i Honda.How should the adapter cord be wired? Should the hot wire be split on the 5-20 to go to each side of the L14-30 plug at the transfer switch?

    Bookmark   October 12, 2011 at 1:45AM
Sign Up to comment
More Discussions
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Sponsored Products
Kenya Rug 4' x 6' - CREAM/CHOCOLATE
$529.00 | Horchow
Area Rug: Presidential Picks Gilreath Ivory 8' x 10'
Home Depot
New Oriental Runner Rare Hand Knotted Wool Balouch Blue Medallion Rug P2
BH Sun Inc
Forest Hanger - Set of Four
$8.99 | zulily
Track Circular Dining Table in Black
$159.00 | LexMod
Haeger Potteries Large Bristol Yellow Ceramic Table Lamp
Lamps Plus
Haeger Potteries Saffron Bristol Bottle Ceramic Table Lamp
$89.91 | Lamps Plus
7873 Opal Frost Bronze Two-Light Bath Fixture
$211.50 | Bellacor
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™