Above Ground Conduit

tonys_2009October 31, 2012

Hello. I'm thinking about putting a spa in my backyard. The problem I'm running into is where to run the conduit. I only have a 5ft setback on the side of my house and the pad for my A/C units takes up most of that space. I don't think there will be enough room between it and the property line to bury a conduit. Is it OK if I ran PVC conduit along the foundation past the A/C pad and then went underground? I considered running the wires through the attic but since the spa requires a full size ground I can't use romex and conduit would be a real pain.

Thank you for reporting this comment. Undo
Ron Natalie

You can use conduit above ground provided that it is rated for how you want to use it (i.e., if it's going to be outside above ground it has to be rated for sun exposure. Note you need to use conductors rated for wet locations (underground is always considered wet and I suspect your overground runs are sufficiently exposed to be considered so as well).

You have a couple of misconceptions here. Unless you have some local code that says otherwise there's no requirement for "a full sized ground" just one that's at least 12gauge and appropriately sized for the circuit. What is required is that it be insulated. However, if we're talking about a single family home, there's an exception that allows you to use a bare ground that's enclosed inside the sheath of a cable (e.g., romex) for the part of the circuit that's inside the building.

    Bookmark   October 31, 2012 at 10:22AM
Thank you for reporting this comment. Undo
tonys_2009

The instructions for the hot tub said it has to be a full sized ground. If I can get away without it I might just run 6/3 through the attic to the spa panel on the side of the house and then run separate conductors from there through underground conduit to the spa.

    Bookmark   October 31, 2012 at 10:42AM
Thank you for reporting this comment. Undo
Ron Natalie

If the instructions for the spa say it's required (rather than recommended) then you have to do it.

Does your spa really require a NEUTRAL? If not, you can use the white wire in the 6-3 on the ground if you remark the exposed sections of the wire you're using as ground green.

    Bookmark   October 31, 2012 at 11:20AM
Thank you for reporting this comment. Undo
kudzu9

tonys-
Regarding your original post, I'm a little confused. Conduit does not take up much space. Why can't you just put conduit in the ground next to the pad, or even run it under the edge of the pad by just digging down and in a little?

    Bookmark   November 1, 2012 at 1:26AM
Thank you for reporting this comment. Undo
tonys_2009

I would run it right next to the pad but there is a stone retaining wall all the way up against the cement. That wall takes up every bit of space between the pad and the property line. I'm scared if I dig under it the foundation for the wall would be compromised.

    Bookmark   November 1, 2012 at 9:28AM
Thank you for reporting this comment. Undo
tonys_2009

I know its been a while but I've been busy and haven't had a chance to mess with this. I was thinking about it a little more and have another question. Isn't rhe full size ground only required from the spa to the spa panel on the house or all the way back to the main panel? Seems to me that the wiring wouldn't make a difference between the spa panel and the main panel. It would be the same as me wiring in the spa to a sub panel correct? I know that they don't use a full 6AWG ground. It would be nice to be able to run 6/3 romex through the attic to the spa panel on the side of the house and then conduit with individual conductors to the spa.

    Bookmark   December 7, 2012 at 3:02PM
Thank you for reporting this comment. Undo
brickeyee

Use rigid metal or intermediate conduit and you only need 6 inches of cover

    Bookmark   December 8, 2012 at 12:51PM
Sign Up to comment
More Discussions
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™