OK to mount GFCI outlet lower than bathroom vanity top?

cinnamonsworldSeptember 21, 2010

We'd like the power outlets to be just lower than the top edge of our vanities, off to the side. Is there any code problem with that height? So many bathrooms have higher ones.

Thank you for reporting this comment. Undo
Ron Natalie

As long as you're within 3' of the sink...

(D) Bathrooms. In dwelling units, at least one receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop, located on the countertop, or installed on the side or face of the basin cabinet not more than 300 mm (12 in.) below the countertop. Receptacle outlet assemblies listed for the application shall be permitted to be installed in the countertop.

    Bookmark   September 22, 2010 at 8:41AM
Thank you for reporting this comment. Undo
cinnamonsworld

Thank you... that is really helpful

    Bookmark   September 22, 2010 at 9:39AM
Thank you for reporting this comment. Undo
petey_racer

The wording here is pretty weird, but it is within 3' of the sink and no more than 12" below the counter level.

    Bookmark   September 22, 2010 at 3:13PM
Thank you for reporting this comment. Undo
Ron Natalie

You have to be 3' from the one edge of (each) sink. The 12" below counter level only applies when you are mounting the receptacle in the cabinet itself. If it's on a wall adjacent to the cabinet, you can mount it anywhere as long as you stay within the 3'.

    Bookmark   September 23, 2010 at 6:51AM
Sign Up to comment
More Discussions
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
Too much load for circuit?
I have 200 amp service to the main panel (which has...
zver11
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™