equivalent load carrying

jmmmmSeptember 21, 2013

I'm running #8 wire out to my 110V, 19 amp lakeside pump (per manufacture recommendation based on the distance from box to pump). Rather than hard wire the pump, I'd like to use a 20 amp GFI and plug. The GFI will accept two #12 wires line wires. Will two #12 carry the equivalent load of the one #8? Is it better to 'unravel' the #8 and split it into two and attaching each to the GFI?

Thank you for reporting this comment. Undo
Ron Natalie

If the manufacturer recommends #8 there is most likely good reason. Motors frequently are not happy with the voltage drop that smaller conductors over longer distances will bring. #12 and a 20A circuit is marginal for something that claims to draw 19A. I can almost guarantee you're going to trip the breaker from time to time. What circuit rating does the manufacturer recommend?

No you CAN NOT parallel #12.
No you can not "unravel" the #8. If the plug or terminal won't accept wire that large, you're going to have to make a connection using some listed means (they do make wire nuts that large, for example) to join to a wire that fits.

    Bookmark   September 22, 2013 at 8:57AM
Sign Up to comment
More Discussions
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™