dim LED at lamppost when "off"

homeboundSeptember 6, 2012

I'm a handyman asking this on behalf of one of my clients.

They have installed an LED bulb in an outdoor lamppost which is on a digital timer switch (Intermatic, I think). When the timer-switch is off, the bulb still glows faintly. Is this normal and can this be prevented? They are concerned about wasting any energy at all. Thanks much.

Thank you for reporting this comment. Undo
Ron Natalie

Get a different timer. There are intermatic timers that use a switch rather than a semiconductor circuit. Sometimes they look identical to the incandescent-only ones. You have to read the ratings (they'll typically be good for fluorescent and small motors).

    Bookmark   September 7, 2012 at 8:26AM
Thank you for reporting this comment. Undo
homebound

Much appreciated.

    Bookmark   September 7, 2012 at 11:45AM
Thank you for reporting this comment. Undo
lbpod

I agree. Sometimes there is something to be said
about the old fashioned mechanical contacts.

    Bookmark   September 7, 2012 at 3:29PM
Thank you for reporting this comment. Undo
homebound

Just to clarify, is there a digital switch, intermatic, that does not have the semiconductor, or are you referring to a different type, eg. the one with the little dial?

    Bookmark   September 8, 2012 at 12:09PM
Thank you for reporting this comment. Undo
Ron Natalie

I don't know which one you have, but Intermatic makes essentially the same electronic timer (with dusk to dawn or timed) available with either an incandescent only (semicondulctor) or more general (motorized switch). They look identical from the outside. I had the former and my CF fixtures flickered when off as well. All was well after I switched.

Here is a link that might be useful: Intermatic timers

    Bookmark   September 8, 2012 at 3:56PM
Thank you for reporting this comment. Undo
alan_s_thefirst

It is normal, with a conventional bulb you just can't see it, but it's consuming current.

As others said, 'electronic' switches always have a little leaked current. A relay, or a mechanical switch is the only solution.

That being said, it probably won't hurt an LED.

    Bookmark   September 10, 2012 at 2:41PM
Thank you for reporting this comment. Undo
brickeyee

"That being said, it probably won't hurt an LED. "

The LED is not the issue, the AC-DC power supply operating the LED can be damaged.

    Bookmark   September 11, 2012 at 10:13AM
Thank you for reporting this comment. Undo
alan_s_thefirst

By the switchmode supply, as per another thread? I can see that. Whilst an incandescent bulb is in there, there's still current being drawn, except bulb is just acting like a resistor, not a bulb.

I guess I should have qualified it by saying OP must verify timer is compatible with LED and/or CFL.

The same topic seems to be coming up, over and over.

    Bookmark   September 12, 2012 at 4:39PM
Thank you for reporting this comment. Undo
brickeyee

Or the CFL or LED must be compatible with an 'conventional' dimmer for it to operate from a typical solid state switch.

    Bookmark   September 13, 2012 at 8:17AM
Sign Up to comment
More Discussions
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™