Armoured Cable

leslie_gardenerSeptember 12, 2011

I'm connecting a short length armoured cable to NM cable in a junction box.

In my reading I see that I have to wrap the bare wire, bonding wire, in the AC around the armour and not to attach it to the ground screw in the box.

I'm puzzled...what is the disadvantage to grounding it to the box?...seems to be the same to me, metal to metal to metal...for my education, what's the difference please?

Thank you for reporting this comment. Undo
brickeyee

You do not have to wrap the bonding wre around at all.

You can just cut off flush before installing the required anti-short bushing (for type AC).

They anti short bushings are usually the little red split sleeves.

They go between the wires and the armor.

Be sure to use the correct cable clamps for type AC.

NM clamps are NOT correct.

The bonding conductor is only there to ensure a continuous ground from the armor (the grounding conductor for type AC cable).

Only one wire can be under a screw head, and you will need to use the hole in the box for the NM grounding conductor.

You must use a metal box with type AC.

    Bookmark   September 12, 2011 at 9:06PM
Thank you for reporting this comment. Undo
mike_kaiser_gw

Brickeyee,

I was under the impression that with AC the bonding strip was folded back along the armored jacket and essentially "captured" by the clamp, not cut flush at the end of the jacket.

Leslie,

Early on armored jacket of functioned as the grounding conductor but over the years they've determined that the ability of the jacket alone to function as the grounding conductor was insufficient so they added a small strip of aluminum to augment the current carrying capacity of the jacket. The rules say that the bonding conductor is not to enter the box.

I'm sure that Brickeyee will chime in here but I'm, too, curious what would happen in a fault if the bonding conductor was tied to the box.

Brickeyee is correct in that NM (aka Romex) clamps look very much like AC clamps but they are not interchangeable. Make sure you use the correct clamps.

    Bookmark   September 12, 2011 at 11:05PM
Thank you for reporting this comment. Undo
Ron Natalie

Mike:

It is NOT necessary to do anything with the bonding strip. It's OK, to do what you want, but what brick suggests is perfoectly acceptable. This explanatory text is in the NEC handbook:

The armor of Type AC cable is recognized as an equipment grounding conductor by 250.118, and the internal bonding strip required by 320.100 can simply be cut off at the termination of the armored cable, or it can be bent back on the armor. It is not necessary to connect it to an equipment grounding terminal. It reduces the inductive reactance of the spiral armor and increases the armor's effectiveness as an equipment ground. Many installers use this strip to help prevent the insulating (anti-short) bushing required by 320.40 (the "red head") from falling out during rough wiring.

    Bookmark   September 13, 2011 at 7:51AM
Thank you for reporting this comment. Undo
leslie_gardener

Thanks for the replies but my question hasn't been answered.
NEC says,"It is not necessary" to connect it to an equipment grounding terminal
"not necessary" translates to "do it if you want to"
But from what I read the text was emphatic in saying "NOT" to connect it to the grounding terminal.
Along with mike i'm curious as to what would happen in a fault if the conductor was attached to the box.

    Bookmark   September 13, 2011 at 11:55AM
Thank you for reporting this comment. Undo
brickeyee

""not necessary" translates to "do it if you want to" "

It is a waste of time, and yuo can only have a single wire under a screw head.

It is also not going to mix well in a wire nut since it is small and aluminum.

    Bookmark   September 13, 2011 at 1:18PM
Sign Up to comment
More Discussions
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™