10/3 Romex with Conduit

ApolloXSeptember 25, 2013

We're wiring a circuit between an electric panel and a disconnect box through the basement and garage. In the basement it can be run along the ceiling beams and does not require conduit piping. In the garage it will be 2 feet off the ground, therefore it does need conduit piping.

Using normal metal EMT conduit and Romex 10/3 NM-B, I had two questions:

1) Can I run a single Romex cable the entire span? If I do, do I need to remove the cover around the Romex cable once it enters the pipe or can I leave it on?

2) What size diameter is required for conduit? The web seems to suggest 1/2 is sufficient, but I've had arguments with a friend of mine who believes 3/4 is required for code in NJ.

Thank you for reporting this comment. Undo
Ron Natalie

I'm unclear as why you think you need conduit.

You should not be running ROMEX inside the conduit. No you CAN NOT just strip the sheath off the NM. If you're going to use conduit, get appropriate single conductors.

1/2" EMT will be fine for up to 5 #10. You may find it easier to go up to 3/4 just to making pulling easier but it's not required.

As near as I know, New Jersey follows the 2011 without any significant modification so 1/2 would be legal.

    Bookmark   September 25, 2013 at 4:26PM
Thank you for reporting this comment. Undo
btharmy

The argument probably stems from the issue of using the 10/3 romex. It won't fit inside a 1/2" conduit with any sort of bends or distance. His friend was trying to tell him it will fit better in 3/4" when in fact it shouldn't be used inside conduit at all. Use thhn individual conductors inside the conduit if you feel you need conduit. Make joints inside and accessable j-box and convert to romex in the basement.

    Bookmark   September 25, 2013 at 6:46PM
Thank you for reporting this comment. Undo
itsunclebill

NM-B (Romex) needs to be installed so it isn't "subject to damage". Most AHJs (building officials) consider anything under 4 feet off the floor in a garage subject to damage if not in a finished wall.

NEC 334.15 (B) specifically permits EMT to be used for this. The EMT shouldn't be used as a "system", meaning the NM-B both enters and leaves the EMT in a fashion that the EMT is used as a sleeve. The EMT shouldn't have boxes on both ends of the run so it is considered a "complete" conduit run.

The installation the OP describes isn't unusual and becomes a problem only if the EMT terminates in the panel or boxes (because of clamping requirements). If the EMT is on a basement wall the rules change slightly.

    Bookmark   September 25, 2013 at 8:43PM
Sign Up to comment
More Discussions
Re-wiring range to service spa
what connectors are appropriate for joining 6-3 NMB...
justsomeotherdude
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
ARGH! no boxes
Went over to my daughter's house to help them change...
Ron Natalie
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
Ceiling fan wiring
I have a new ceiling fan with a light. The fan has...
jjp2121
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™