Outdoor GFCI receptacles

ylmzmSeptember 4, 2013

I plan to install some outdoor receptacles around my backyard. There will be 4 quad receptacle boxes. Each box will have 2 duplex receptacles, each on a separate circuit (2 circuits will feed all 8 duplex receptacles, 4 duplex per circuit).

Since these are outdoor receptacles, they need to be GFCI protected. I see a few options:

(1) Multi-wire circuits, connected to a non-GFCI circuit breaker, all receptacles are weather resistant GFCIs.

(2) Multi-wire circuits, connected to a GFCI double pole circuit breaker.

(3) Regular circuits, connected to non-GFCI circuit breakers, all receptacles are weather resistant GFCIs.
(4) Regular circuits, connected to GFCI circuit breakers.

Which option would you recommend? I will use #8 THHN wires (in PVC conduits), so I would like to save some wire if possible. The distance from the panel to the furthest receptacle is about 150 feet.

Couple of more questions:
(1) Can I use a single ground (#8) wire for both circuits?
(2) If I use all 20-Amp receptacles, can I use a 20-Amp breaker, or should I use a 25-Amp breaker?

Thank you for reporting this comment. Undo
    Bookmark   September 4, 2013 at 2:19PM
Sign Up to comment
More Discussions
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™