I replaced a Westinghouse EP Single Phase S10N05S51B 120 X 240, 12 X 24 Transformer, which was used to power out in-ground poolâÂÂs light with a Westinghouse S10N0551A. Before disconnecting the old transformer, I took photos of the connections to be sure I connected the new one correctly which are:

H1H3 (Black In)
H2H4 (White in)
X1X3 (Black out)
X2X4 (White out)
Ground in to ground out.

I am positive I connected the new transformer exactly like the old one and, with the IN wires connected and no wires attached to the OUT side, power is being sent out through X1X3.

My problem is, every time I connect ANY wire (the actual load wires or a spare piece of wire) to X1X3 or even X2X4, the X1X3 wires stop sending power out. When I remove the wire, then X1X3 will again send power out. For the life of me I canâÂÂt figure this out. Anyone have any ideas what IâÂÂm doing wrong?

Thank you for reporting this comment. Undo
randy427

Have you tried calling Westinghouse's customer service?
(888) 417-6222 for lighting

    Bookmark   August 5, 2013 at 4:56PM
Thank you for reporting this comment. Undo
Ibewye

How are determining power is being sent out and not sent out?

    Bookmark   August 5, 2013 at 11:18PM
Sign Up to comment
More Discussions
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Where to find power connectors for the LED under cabinet lights?
I bought a set of the GE/Jasco LED under cabinet lights...
flyingkite
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™