I have a 220v portable welder. The problem I have is that not every place I take it has an appropriate receptacle to plug it in to. I have an idea to make and adapter for this. I would use a junction box with the appropriate 220 receptacle and have 2 short whips feeding it, each with a 110 male plug on the ends. If I were to run a heavy gauge extension cord from each whip to different 110v outlets (each of which was fed by one of the 2 different legs in the circuit panel)Then I would have 220v at the adapter, right? Breakers in the odd number column of the panel are on one leg and even numbered breakers are on the other leg. So if "Living Rm" is breaker "12" and "Laundry" is breaker "9", then running one of the extension cords to each of these rooms should work. Am I looking at this correctly? Is there any reason not to do this?

My next question is amperage. If the above can be done, how is the amperage figured? If each of the (2) 110v circuits are 15a, does that give a 30a rating after the 2 legs are combined through the 220v receptacle, or does it remain 15a? Thanks for any input.

Thank you for reporting this comment. Undo
brickeyee

"If each of the (2) 110v circuits are 15a, does that give a 30a rating after the 2 legs are combined through the 220v receptacle, or does it remain 15a?"

It remains 15 A at 240 V.

Unless you have a small welder, not a great idea since it will overload the 15 A circuits (and probably trip them off as soon as you try to strike an arc).

    Bookmark   August 19, 2011 at 5:40PM
Thank you for reporting this comment. Undo
fixizin

They make welders that run on standard 120V. Sorry, you probably didn't want to hear that.

I used to sketch out jury-rigs such as yours... luckily someone wiser was always around to say "put down the pencil, back away slowly..."... lol.

    Bookmark   August 19, 2011 at 6:18PM
Thank you for reporting this comment. Undo
wildbill2374

The welder is in excess of the 15a that the standard 110 circuit would provide. I know of the 110v portable mig welders, but the higher voltage ones can weld heavier thicknesses of metal. If the (2) 110v legs combined only offer the amps rated to a single leg, then I guess the Idea is dead in the water....Hypothetically speaking though, does the rest of the idea hold water? Is there any other reason that you can't link the two 110v outlets (fed by the (2) separate legs in a circuit panel) to make a 220v portable outlet?

    Bookmark   August 19, 2011 at 11:07PM
Thank you for reporting this comment. Undo
mike_kaiser_gw

It's a bad idea. Buy a 120v welder or a gas powered welder and long cables.

    Bookmark   August 20, 2011 at 8:26AM
Thank you for reporting this comment. Undo
brickeyee

"I used to sketch out jury-rigs such as yours... luckily someone wiser was always around to say "put down the pencil, back away slowly..."... lol."

It can actually work if you only need 15 A at 240 V.

When doing refrigeration work there is often not easily available 120 V to run a vacuum pump (or recovery equipment) since the requirement for a 120 V receptacle near a compressor/condenser is relatively new.

Running from one leg to ground at the outside disconnect is pretty common.

    Bookmark   August 20, 2011 at 10:41AM
Thank you for reporting this comment. Undo
groundrod

all of the conductors of a circuit must be contained in the same conduit or cable etc...

    Bookmark   August 20, 2011 at 10:52AM
Thank you for reporting this comment. Undo
wayne440

A good way to get someone killed. When the welder is "on", removing one of the 120V plugs may yield a nice suicide cord, the plug blades will be hot.

I solved part of a similar problem by making adapter pigtails with common 240V range/dryer/AC plugs and a welder receptacle. Still probably not 100% "to code", but not nearly as dangerous as a pair of 120V plugs.

    Bookmark   August 20, 2011 at 11:39AM
Thank you for reporting this comment. Undo
brickeyee

"all of the conductors of a circuit must be contained in the same conduit or cable etc..."

That does not say anything about utilization equipment that is cord and plug connected.

There are numerous ways to rig a device like this that prevent exposure to a male plug with any voltage present.

    Bookmark   August 20, 2011 at 2:43PM
Thank you for reporting this comment. Undo
enigma_2

Why not consider purchasing a 120v-240v transformer? A 5000 watt unit will run around $150 and you could use it on any job site. One example is on link below.

Here is a link that might be useful: 5000 Watts Step Up - Step Down Transformer

    Bookmark   August 29, 2011 at 5:19PM
Sign Up to comment
More Discussions
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Code changes
In outlining the electrical layout for our new home,...
mtvhike
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Sponsored Products
Bath Authority DreamLine Duet Sliding Tub Door (56"-60")
Modern Bathroom
Uttermost Ogden 37" High Wall Mirror
Lamps Plus
Earth Drop Table Terrarium - Medium
$49.99 | Dot & Bo
French Handle Oil Rubbed Bronze Widespread Bathroom Faucet
Overstock.com
Calypso Area Rug
Home Decorators Collection
Jaipur Maroc Nada 2'6" x 8' Canterbury, Orange Rug
$177.00 | PlushRugs
Nemo Italianaluce | Logo 300-5 Floor Lamp
$864.00 | YLighting
McAdams 1-lt Outdoor Hanging Pendant
LBC Lighting
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™