ingound poolpump circuit question

pittpeteAugust 20, 2010

Im wiring a 1 HP 220v pool pump located next to my house and 25'+ from the pool water.My plan is to run 12-2 UM w/ground to a PVC junction box inside my unfinished bsmt before I punch outside.The pool pump circuit will come off the main(2 pole 20 AMP GFCI breaker) into a 2 pole Intermatic timer and run 40' to the junction box.

My question is can I switch over to THWN from the junction box go through the wall into PVC tubing down to the poolpump outlet(mounted on side of house),220 V 20 AMP rated twistlok receptacle and 3' SJ cord into poolpump motor?? The reason being is Id have to drill through the foundation to account for the 3' requirement of the cord.

Thanks for any responses

Thank you for reporting this comment. Undo
manhattan42

Everything should be fine except:

-SJ cord is not rated for damp locations only. Can't be used in wet locations.

-Depending on your Code, you may be restricted to having the pump motor wired using flexible conduit only. (IRC electrical provisions permit twist-lock cords on permanently installed above ground pools only.)

    Bookmark   August 21, 2010 at 11:35AM
Thank you for reporting this comment. Undo
manhattan42

The above should read: "SJ cord is rated for damp locations only"

    Bookmark   August 21, 2010 at 6:30PM
Thank you for reporting this comment. Undo
petey_racer

I think the term "SJ cord" is generic for flexible cord. Most cords like this are typically "W: rated as well.

"-Depending on your Code, you may be restricted to having the pump motor wired using flexible conduit only. (IRC electrical provisions permit twist-lock cords on permanently installed above ground pools only.)"

I have never heard of any requirement, even local, that requires a conduit-only connection to a pool pump motor. Of course it may exist somewhere, but in all my years i have never heard of such.
Also, there is no distinction between above-ground and in-ground pools. Just storable and permanently installed.
A twist lock connection for a pump motor is allowed in any installation. The only limiting factor is the distance the receptacle is from the pool.

    Bookmark   August 22, 2010 at 9:40AM
Thank you for reporting this comment. Undo
manhattan42

Petey is somewhat right.

Twist lock receptacles are allowed for any permanently installed pool pump motor installation but are only usually found supplied with non-storable type above ground pools.

Twist lock receptacles cannot be used with storable swimming pools. Storable swimming pool cords come with their own factory supplied grounded attachement plugs that are required to have a built in GFCI protection device.

-----------
"SJ" cords may be referred to generically, but a labeld "SJ" cord cannot be used in this case because they are only listed for use in damp locations.

    Bookmark   August 22, 2010 at 1:04PM
Sign Up to comment
More Discussions
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Oil in Motor of Ironrite Rotary Iron. what do I do now?
Hi, I just bought an old 1946 Ironrite rotary iron...
lucinda002
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Electrical Problem.
My mom's house has a problem with the lights temporarily...
Debra Johnson
Sponsored Products
Nelson | Lotus Floor Lamp - Cigar
$399.00 | YLighting
Crescendo Large Satin Nickel Fourteen-Light 36-Inch Chandelier with White Flight
Bellacor
Indiana Hoosiers 20-Oz. Mason Jar & Lid
$9.99 | zulily
One Circuit Monorail End Power Feed
LBC Lighting
Americh Catalina II 6042-2 Tub (60" x 42" x 22")
Modern Bathroom
AICO Furniture - After Eight Media Cabinet Titanium - 19081-16
Great Furniture Deal
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™