converting 1 way switches to 3 way switches.

timelinexAugust 10, 2013

I moved into my 'new' house(1994 house) a couple months ago and the switches have been driving me crazy.

There are many places where two switches control the same light, except it doesn't work the right away. For one switch to turn on the light, the other had to of been left in the on position, and vice versa.

After some googling, I figured out that its because I most likely have 1 way switches that are just put in series. Great.

This occurs a bunch of tiimes throughout the house(walk in closet,hallways,upstairs/downstairs controlling same lame etc..)

What can I do to fix this?

I opened up a light switch in the closet. Inside the light switch box, I have a red, black wire going to the switch. Then I have a black ground wire going to the screw on the switch. Inside the switch box I also have a white wire thats twisted off to another white wire. I can take a picture and post it if necessary.

How can I remedy this and install a 3 way switch on each side.

Any help would be greatly appreciated!

Thank you for reporting this comment. Undo
jreagan_gw

Did you mean "bare" ground wire, not "black" ground wire?

If you have a white/black/red conductors then you seem to have the needed 3-conductor wire.

And the switch only has two connections on it? (not counting the ground wire).

I find it odd that somebody went to the trouble of putting in a 3-conductor wire but only using single-pole switches.

    Bookmark   August 10, 2013 at 2:37PM
Thank you for reporting this comment. Undo
timelinex

The ground wire is in fact surrounded by black plastic, just like a regular wire would be. However, it is obviously stripped at the tip and is going around the grounding screw.

Yes, the switch only has two connections. The black and red wire.

There is actually a bare grounding wire that is attached to another bare grounding wire. I attached an image showing the entire setup.

So what wire do I place where, if I get a 3 way switch?

    Bookmark   August 10, 2013 at 2:51PM
Thank you for reporting this comment. Undo
Ron Natalie

I think some idiot replaced the three way switch with a two way (possibly the original 3-way wasn't grounded). The bare wires are the grounds. It is ILLEGAL to use black for the ground.

If there are indeed other grounds in the cable (bare), pig tail one of those out and use the black wire as the second traveller.

    Bookmark   August 10, 2013 at 5:16PM
Thank you for reporting this comment. Undo
timelinex

So, from the picture that I posted what wire am I suppose to use as the first traveler, second traveler, ground and common?

    Bookmark   August 10, 2013 at 6:43PM
Thank you for reporting this comment. Undo
bus_driver

We are left to guess how this occurred. One is that "Mr Homeowner Previous" did this. At the least we must assume that he lived with this arrangement for some period of time-- perhaps as long as 19 years.
Installing the actual receptacles and switches on new installations is called "trim-out" and is often assigned to the newest and least experienced employees. And some companies pay for the trim-out by piece-work-- so much for each installed. The more installed per hour, the higher the effective pay rate. Has some advantages but is definitely not conducive to quality workmanship.
I suggest that you become very familiar with 3-way circuits and with the proper installation of equipment grounding conductors before personally doing any more to this situation.
Or hire a trusted electrician.

Here is a link that might be useful: Book

    Bookmark   August 10, 2013 at 7:23PM
Thank you for reporting this comment. Undo
timelinex

So then no feedback on which wire where then...

    Bookmark   August 10, 2013 at 10:08PM
Thank you for reporting this comment. Undo
hendricus

There is no way to tell which wire goes where until it is figured out where each wire comes from (power, the other switch, light) and which actually are the feed wires or travelers. Only an examination of the whole setup will determine what goes where.

    Bookmark   August 11, 2013 at 12:07AM
Thank you for reporting this comment. Undo
randy427

If you can post a diagram of the wires coming into each junction box, both switches and the light fixture, we can probably tell you which is the most likely solution. There are several possible variations, otherwise.
Does the power supply cable come into the fixture first or to one of the switches? If to a switch, does the cable to the fixture come into that switch or the other?
With that diagram and a decent DIY book, you might also figure it out yourself.

    Bookmark   August 11, 2013 at 7:38AM
Thank you for reporting this comment. Undo
elltwo

What do things look like in the other switch box in the closet you are talking about?

Harder to see is what wires enter and exit the box at the light.

The simplest set-up for a home owner to deal with will have a single gang box with one non-dimming 3-way switch at each location, and just one (black/white/bare ground) cable and one (black/red/white/bare ground) cable in the box with the switch.

The cable that contains the red should go from box to box and makes up the travelers. The black and red ends of this cable should land on the screws on the switch that are the same color as each other (usually not black).

The other cable either comes from the panel (the feed in) or goes to the light (the feed out). Put the black from this cable under the unique colored screw (usually black and sometimes called the common or point). Splice together all of the white wires and use the bare ground to ground each other and the switch and the box if it's metal.

If you have a different wire arrangement than this, (and there are several that are both different and correct), and if you have only a small amount of experience then you would probably be well served by hiring a pro.

I personally can't recall ever seeing or installing a 3-way in a walk-in closet and the black conductor landed on the ground screw makes me think that you will end up hiring someone to sort this out. Good luck.

    Bookmark   August 12, 2013 at 7:27AM
Thank you for reporting this comment. Undo
btharmy

My guess is that the yoke of the new switch is energized depending on the position of the other switch in the loop. He installed single pole switches in place of old 3 ways and landed either the hot or traveler on the ground screw. Call an electrician. It won't take him long to fix this.

    Bookmark   August 13, 2013 at 10:39PM
Thank you for reporting this comment. Undo
mikecowley

Is it possible that there is a back-stab at the left hand side of the switch picture? Is it also possible that the black wire attached to the ground screw is actually hot, or possibly just hot when the other switch is toggled? The other switch has the same black wire going to a ground lug?

    Bookmark   August 15, 2013 at 6:06PM
Thank you for reporting this comment. Undo
bcarlson78248

There may be no way to fix this by simply re-wiring one switch. This switch is wired wrong and they may have made wiring changes in other areas to compensate. A decent electrician should have no problem figuring it out, but he/she will need to look at all the switches and lights before making any changes. The good news is that they apparently did use 3 wire cable, so the conversion to 3 way control can probably be done by swapping switches, without any other big modifications.

Bruce

    Bookmark   August 30, 2013 at 6:18AM
Sign Up to comment
More Discussions
Need to Understand GFCI Requirements.
I posted this in the remodeling section, but I think...
homechef59
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Code changes
In outlining the electrical layout for our new home,...
mtvhike
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Sponsored Products
Hansgrohe - 6 Inch Baseplate For Euroaktiv 1-Hole Lavatory - 06490000
$20.00 | PlumbTile
Monorail 600W 24V Surface Mount Magnetic Transformer
Lightology
Simmons Kids Chevron 4-in-1 Convertible Crib-N-More - 319180-054
$399.99 | Hayneedle
Innovation USA | Sly Deluxe Sofa, Chrome Base - Quickship
YLiving.com
Home Decorators Collection Chandeliers Rogen 3-Light Oil Rubbed Bronze Small
Home Decorators Collection
Jonathan Adler Parker Brass Plug-In Swing Arm Wall Lamp
Lamps Plus
Somerton Blacksmith Two-light Semi-flush Convertible Fixture
Overstock.com
Lithonia Lighting 4 in. Recessed GU10 Nickel Gimbal Kit LK4GBN
$20.97 | Home Depot
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™