Where can I find proof?

jscozzAugust 21, 2012

I know very well that a GFCI does not require a ground to work... but I need to convince an inspector that this is the case. He only sees that it does not trip with his tester... which I know is using the ground to trip it... as opposed to the built in test button that uses the neutral. And I know it is perfectly legal and code compliant to have a GFCI in an old house which does not have aground, in order to meet the 6ft kitchen GFCI code. But the inspector (not electrical inspector... but rental habitability inspector) is asking for proof or statement from an electrician. Is there a section of the NEC that states this is code compliant I can refer him to?

Thank you for reporting this comment. Undo
bus_driver

Article 406.4 (B) Exception No, 2, 406.4 (D)(2)(b) and (c). The NEC is more definitive than the statement of any electrician. I suspect that the inspector will have difficulty understanding the language. If the inspector was truly worthy of his position, he would already have learned this information of his own volition.

    Bookmark   August 21, 2012 at 11:02AM
Thank you for reporting this comment. Undo
Ron Natalie

Yes, Bus is right. Make sure you've appropriately marked (the GFCI's often come with labels in the packaging) the protected receptacles with "No Equipment Ground" on all protected receptacles (even the GFCI itself) as well as "GFCI Protected/No Equipment Ground" on any downstream protected receptacles.

Actually both the exception in 406.4(A) and the exception #2 in (B) apply here. I'd highlight both exceptions and the text in 406.4(D)(2). You might be able to get the local electrical inspector to concur which ought to have weight.

    Bookmark   August 21, 2012 at 11:08AM
Thank you for reporting this comment. Undo
petey_racer

If this clown is asking for this he has NO place doing inspections like these.

    Bookmark   August 21, 2012 at 7:40PM
Thank you for reporting this comment. Undo
jscozz

Thanks for the info. Luckily the electrical inspector let the rental inspector know that it was OK as is. So I did not have to throw the code section at him... thank you all for your help.

    Bookmark   August 21, 2012 at 8:49PM
Thank you for reporting this comment. Undo
bus_driver

My post used the word "volition". While not necessarily incorrect, the better choice would have been "initiative".

    Bookmark   August 22, 2012 at 2:40PM
Sign Up to comment
More Discussions
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
Lights Flickering...
We paid an electrician to put in a ceiling light in...
regina_phalange
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™