Splicing Wiring or Run New Due o Vandalism

Pete33July 26, 2012

I am building a new home and a theif in the night cut off and stole all of the electical wiring leading to where the breaker panel would eventally be located and stole the last 12' of each wire (about 40 wires total). All of the wiring in the house was basically cut about 12' from the panel. What can be done, short of re-wiring the whole house? Can j boxes be installed to splice? Is that safe? If we were to splice and install about a half dozen j-boxes, they would have to be in my child's bedroom, and want to be sure that wont cause me any future problems. Alother not, the rough elec inspecion was passed already and all work was done by a licsence electrician

Thank you for reporting this comment. Undo
bus_driver

The only practical solution is to start over. Don't splice those cables.

    Bookmark   July 26, 2012 at 10:05PM
Thank you for reporting this comment. Undo
brickeyee

Splice MUST be in accessible junction boxes.

You must replace the cables or spend even more money on adding accessible junction boxes at every existing junction box.

'Accessible ' means after the finished wall is created, no damage is done to the wall to access the box.
Every one would need a blank cover plate.

    Bookmark   July 27, 2012 at 11:26AM
Thank you for reporting this comment. Undo
ionized_gw

Will someone's insurance cover this?

    Bookmark   July 27, 2012 at 1:51PM
Thank you for reporting this comment. Undo
Pete33

I have a builder's risk policy with a $1000 deductable, but would not want to turn it in to mine if I can avoid it.

If junction boxes if the recommended fix by the electrical contractor, how many splices pet box are allowed?

    Bookmark   July 27, 2012 at 4:54PM
Thank you for reporting this comment. Undo
ionized_gw

The number of splices per box depends on the size of the box and is clearly regulated by "box fill' specifications. You are going to end up with a bunch of visible box cover in that bedroom if you go this route.

    Bookmark   July 27, 2012 at 8:54PM
Thank you for reporting this comment. Undo
alan_s_thefirst

Those bastards. You absolutely don't want to splice - no way. It would be a huge shadow cast over any future sale.

Consider this - very few wires are home run, so you'll be replacing the wire from the panel to the first connection, ie the first device in the chain.

Needless to say you'll want to beef up your security!

Where I am, scrapyards are required to see ID when purchasing copper (and other) scrap now, I'd be campaigning to have similar laws.

Regardless you'll need another inspection, and I doubt they'd be impressed with a bunch of splices. Talk to your electrician, maybe they'll come to the party and you won't need to use your insurance (if it's around the deductible?) but that's what it's there for.

As the saying goes, "why spoil the ship for a ha'porth of tar?"

    Bookmark   July 29, 2012 at 1:24PM
Sign Up to comment
More Discussions
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™