I'm doing work to finish a section of my basement (all permits properly pulled!). At my rough electric inspection, the inspector alerted me to the new bonding requirements for the flexible gas lines in my house (CSST). I understand the requirements, but have a couple of additional questions.

1. He noted that 6awg wire is required for my situation. Because the gas entrance is at the other end of my basement from the common ground, I intend to use insulated THHN/THWN wire. I don't like the idea of 60 feet of bare wire acorss my basement. Stranded THHN/THWN seems much more common and appears to meet the necessary specs. Does NEC say whether I should use stranded or solid for bonding?

2. I seem to recall that single wires need to be in a conduit. Does code require that I put this single insulated bonding wire in conduit? The entire run will be accessible, if that matters.

Thanks very much for the information.

Thank you for reporting this comment. Undo
petey_racer

Stranded or solid, bare or insulated. it's your call.
No conduit is required or needed. Just keep it out of harms way.

I am not sure why the idea of bare wire scares you. This is typical for any bond or grounding electrode conductor wire.

    Bookmark   July 25, 2010 at 10:59PM
Thank you for reporting this comment. Undo
petey_racer

Stranded or solid, bare or insulated. it's your call.
No conduit is required or needed. Just keep it out of harms way.

I am not sure why the idea of bare wire scares you. This is typical for any bond or grounding electrode conductor wire.

    Bookmark   July 25, 2010 at 11:00PM
Thank you for reporting this comment. Undo
bobinbaltimore

Thanks, Petey. Bare wire doesn't scare me, but I like the idea of having a jacket so that in the case of a fault there is less likely to be inadvertent energizing of metal in incidental contact with the ground (like sheet metal used in creating cold air returns between joists that are along the path of this wire). Call it a little comfort level, that's all.

    Bookmark   July 26, 2010 at 6:04PM
Sign Up to comment
More Discussions
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Wiring in a 1 1/2" thick wall cavity
I need to run 12/2 wire thru an existing thin wall....
baker1mich
Can I electrify battery-operated lights?
Hi all. Is there a way to electrify a battery operated...
eam44
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Electrical Problem.
My mom's house has a problem with the lights temporarily...
Debra Johnson
Sponsored Products
Juno Misc Cables Pro-Series 6 ft. Light Fixture Cord and Plug White ULH-CP-WH
$6.97 | Home Depot
Lidia Jumbo Metal Swivel Stool with Arms
Overstock.com
Drumbox Table Lamp by Diesel by Foscarini
$912.00 | Lumens
Bover | Maxi-S Outdoor Pendant Light
YLighting
Bath Authority DreamLine SlimLine Single Threshold Shower Base (30" by 60")
Modern Bathroom
Bend Seating | Lucy Counter Stool
YLiving.com
© 2015 Houzz Inc. Houzz® The new way to design your home™