Installed GE Monogram Oven, Electrical Wiring Advice Needed

chiahJuly 19, 2010

First of all, GREAT site! We *almost* finished our kitchen remodeling. During the process, this site was, and still is, the one that we used the most for our research and inspiration.

My questions are for any electrician with experience in California.

We purchased and installed a GE Monogram single wall oven. The manual suggested that it can use either a 120/240v or 120/280Yv circuit. Based on all researches that we did, 120/240v seems to be the right one for Sacramento.

The manual also suggested that if the oven consumes less than 4.8kW, we needed to install a 20amp circuit protection. Given that the oven sticker indicated that it uses 4.5kW on a 120/240v circuit, I installed a dedicated 120/240v circuit with 12/3 NM wire and a double leg, not tandem, 20amp circuit breaker.

Yesterday was the first time that we baked something, at 450F for 15 minutes or so. I have access to the actual wire. Out of curiosity, I touch the wire (might not be the smartest thing to do) and felt that it was a bit warmer than the rest of the wires. Not hot, just a bit warmer.

Even though the breaker didn't trip, I am a bit worried about the temperature.

Should the wire be a bit warm? Is 12/3 sufficient or should I upgrade to 10/3 and keep the 20amp breaker?

Sincerely appreciate any help.

Chia

p.s. I also posted this message in the Appliance Forum.

Thank you for reporting this comment. Undo
Ron Natalie

The installation manual will almost CERTAINLY tell you what they recommend/require for the circuit. The simplest GE Monogram single wall oven does spec a 20A circuit. I'd put the larger wire in anyhow. Someday you might want to put one of the speedcook / trivection things in there that requires a 30A circuit. You might even consider wire big enough for 40A (#8) if you ever think you might put double ovens there.

    Bookmark   July 20, 2010 at 8:12AM
Thank you for reporting this comment. Undo
brickeyee

"double leg, not tandem, 20amp circuit breaker."

What do you mean by "double leg"?

The breaker handles are required to be tied together (2-pole breaker).

    Bookmark   July 20, 2010 at 8:56AM
Thank you for reporting this comment. Undo
chiah

Thanks.

Ronnatalie, the space for the oven is under the counter top. So a double oven is out of question. Also, we came from a double oven to a single oven, so there is already a #8 wire somewhere else in the kitchen that I capped off on both ends (kitchen and sevice panel). Shall we remodel the kitchen again, hopefully not ;), we can always tap into that one. I will pull out the 12/3, put in 10/3 and leave the 20amp breaker in the service panel.

Brickeyee, sorry for the terminology. It is a double pole, the two levers are linked and the breaker occupies two slots in the service panel.

    Bookmark   July 20, 2010 at 1:49PM
Thank you for reporting this comment. Undo
weedmeister

FYI from the other post: this is a 100ft run of #12.

    Bookmark   July 20, 2010 at 8:37PM
Sign Up to comment
More Discussions
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
1 of 2 security light bulbs keep going out, do i need a new light?
I have a security light fixture in my carport that...
tlbean2004
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Sponsored Products
Agee Woodworks Normandy Wood Fireplace Mantel Surround - RICHMOND4840BIRCH
$379.99 | Hayneedle
Abstract Giclee LED Reading Light Plug-In Sconce
Lamps Plus
Sydney Pendant by Tech Lighting
$236.00 | Lumens
Westinghouse Ceiling Fans Oak and Walnut Reversible Fan Blades (5-Pack)
$25.77 | Home Depot
Fusion Clips Square Wall Sconce by Justice Design Group
$196.20 | Lumens
Gama Sonic Posts Imperial Outdoor Black Solar LED Post Light on 3 in. Fitter
Home Depot
Congress Antique Nickel 30-Inch Three Light Bath Fixture with Hand Blown Clear G
$479.00 | Bellacor
Resort Spa Bath Towel
$27.50 | FRONTGATE
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™