Thru the wall a/c unit

Annac43July 19, 2011

Hi I recently purchased a thru the wall a/c unit. Come to find out the a/c wont run do to the outlet n breaker that is currently in place. we have been told that we have to switch out both outlet n breaker..

now my question is can i do this myself. the current breaker in place is a 15a 125v breaker and the outlet is also a 15a 125v. I was told to convert the both to a 20a 220v breaker. is this correct the clerk at home depot told me this.

My husband knows how to replace an outlet but has never had to replace a breaker any help or suggestions would be helpful.

The outlet for the a/c is the only dedicated line to the breaker

Thank you for reporting this comment. Undo
kurto

If the a/c unit requires 20A at 240V, you will need to pull a new 12/2 cable to this location, put in a 240V two pole breaker, and install a NEMA 6-20 receptacle. This will probably mean a bit of rework for the existing circuit as well, since it won't be used at this location any longer, but may need to be rerouted to work with other receptacles.

Without more info about your husband's skill level, I can't answer whether he's up to installing a new circuit or not.

    Bookmark   July 19, 2011 at 4:42PM
Thank you for reporting this comment. Undo
Billl

Replacing the outlet and breaker is easy. The breaker literally pops into place and you just slide the wires into the slot and tighten the screw. (Note: turn the power off at the main disconnect before working in the panel.) You need to make sure you have room for the new breaker though because it will be twice as wide as the current one.

Unfortunately, that is only half the job. Presumably, they ran 14 gauge wire to match the 15amp breaker. If so, you'll need to run a new 12 gauge wire from the breaker box to the outlet. That means fishing wire up through the walls and through whatever obstacles are between that and the panel. Depending on the layout, that could be relatively easy or a total pain.

On the plus side, this is about the simplest circuit you could start out with. Just 1 wire from an outlet to the panel. The only real challenge is getting that wire from point A to point B.

    Bookmark   July 21, 2011 at 9:02AM
Thank you for reporting this comment. Undo
weedmeister

The 220v will require a double breaker, most likely, or two slots in your panel. Hopefully you have room already for this.

    Bookmark   July 21, 2011 at 3:38PM
Sign Up to comment
More Discussions
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Testing a fluorescent bulb
I've got a light box that isn't lighting up when I...
kudzu9
Dryer power cord next to vent
My contractor is enlarging the dryer vent hole in the...
phil2015
Sponsored Products
Real Simple Stardust White Boom Plug-In Swing Arm Wall Light
Lamps Plus
Bianca 24" Wall-Mounted Modern Bathroom Vanity - Zebrawood
Modern Bathroom
Furniture of America Zarina Walnut 6-shelf Wall-mounted Bathroom Tower Cabinet
Overstock.com
C.R. Plastics Porch Rocker In Beige
Beyond Stores
Bedside Lamps: 1-Light Table Lamp Light Blue Finish CLI-LS442998
Home Depot
Trinity 3-Light CFL Wall Light
LBC Lighting
© 2015 Houzz Inc. Houzz® The new way to design your home™