replacing large breakers, how to do it???

jaansuJuly 6, 2011

the 50amp breaker pair for my AC compressor keeps popping open. It has never done this before last week. I'd like to try the potentially cheap fix of replacing the breaker before calling an AC technician. How difficult (and safe) an operation is this? I've done all sorts of electrical work but never on a breaker box. If I throw the main breaker first, do I avoid the worst danger?

Thank you for reporting this comment. Undo
Ron Natalie

It's straight forward, but I would suggest it's most likely a waste of time and money to do so.

    Bookmark   July 6, 2011 at 2:14PM
Thank you for reporting this comment. Undo
kurto

It's not very likely that the breaker is the issue, but it is possible. If you throw the main, then only the lugs where the feeder is connected will be hot (and not protected by a over-current device). To me, the most risk while working in the box is loose ends of wires flopping around and coming in contact with the lugs. Replacing a circuit breaker is a pretty simple operation, and reasonably safe as long as you pay attention to what you're touching.

    Bookmark   July 6, 2011 at 2:19PM
Thank you for reporting this comment. Undo
jaansu

replacing the double breaker was easier than I dared hope and the AC seems to be staying on this time. I do notice that this new breaker has warmed up to 86 F over 90 min, using my laser thermometer to measure the heat. Normal or is something not so good going on? All the other breakers are smaller but only a GFI breaker is as warm as 85 F.

    Bookmark   July 6, 2011 at 8:19PM
Thank you for reporting this comment. Undo
btharmy

Should have spent the $$ toward an amp probe instead. Then you would know how much current the ac is drawing. That is what you should be more concerned with. Fixing the problem, not the symptoms.

    Bookmark   July 6, 2011 at 10:50PM
Thank you for reporting this comment. Undo
brickeyee

breakers are thermal-magnetic.

They use a thermal section to provide a slow trip for short overloads, and a magnetic trip to quickly clear large faults.

Yes they get warm.

The IR thermometers are notoriously inaccurate unless adjusted for the emissivity of the surface being measured.

    Bookmark   July 7, 2011 at 9:48AM
Sign Up to comment
More Discussions
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Humming Transformer
Last summer the POCO replaced the transformer on the...
mike_kaiser_gw
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
Disposer Power Cord
I recently bought a GE disposal online. The model is...
africanboy
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
© 2015 Houzz Inc. Houzz® The new way to design your home™