Can PVC Conduit Cause Overheating?

bshanleyJuly 1, 2011

I'm installing an inlet from outside my home for my transfer switch. I used 10/3 building wire, with a ground. For neatness, I used 1/2" PVC Schedule 40 conduit in two places, one about 5', one about 3'. It was a pretty tight fit getting the wire through. Now I'm wondering, will the tight fit cause overheating? I haven't tried it out yet. Thanks in advance.

Thank you for reporting this comment. Undo
bus_driver

Your direct question is about overheating. No problem in your case. You did install NM cable in the conduit. If the conduit is in a "dry" location, the cable will not suffer from moisture damage. If these were individual conductors in the conduit, the installation would meet NEC specs for "fill". Based on the information you furnished, your installation will function satisfactorily.
Others will be along to debate the use of the conduit with the NM cable.

    Bookmark   July 1, 2011 at 7:15PM
Thank you for reporting this comment. Undo
kurto

Conduit or not, you have a problem if you installed NM (non-metallic) cable, since it isn't rated for wet locations. NM cable will rapidly fall apart under wet conditions (and the inside of conduit is particularly wet). You should have used UF cable or alternatively THWN individual wires inside conduit.

    Bookmark   July 3, 2011 at 8:59PM
Thank you for reporting this comment. Undo
bshanley

Hi Kurto: Thanks for your advice. Let me say a little more, to make sure we're on the same page. I ran 40' of wire. 39' were inside the house, and all the conduit was inside the house. The final foot went through the block (10"), and the last little bit was inside a UL rated box, on the outside wall. I sealed the gap between the house and box on the top and two sides with Silicone II. Does it still sound as bad? How is it materially different than the wiring that runs to the light at my front door, which is not really wired as well? Thanks again - I'm not disputing your advice, just want to learn.

    Bookmark   July 6, 2011 at 12:33AM
Thank you for reporting this comment. Undo
kurto

With the installation you describe, you should be okay. It's technically a violation, but a rather minor one that is pretty common, and shouldn't present any real problems.

    Bookmark   July 6, 2011 at 8:56AM
Thank you for reporting this comment. Undo
Ron Natalie

I don't think it's a violation. The box is not a raceway even if it is in a wet location (though it does need to be rated for such the wires inside do not) and the raceway (conduit) is in not in a wet location.

The conduit provided to protect the NM from physical damage here is acceptable.

    Bookmark   July 6, 2011 at 11:25AM
Thank you for reporting this comment. Undo
kurto

Ronnatalie, I agree if none of the cable is exposed to the elements.

    Bookmark   July 6, 2011 at 2:08PM
Sign Up to comment
More Discussions
Replacing dimmer switch: different wire colors on new switch
My DR lights, which are controlled from two switches,...
msa6
Crawl Space Junction Boxes: inspection and capping
Hello. I'm in the process of crawl space improvement....
SparklingWater
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
A/C wired to main panel only?
I had 2 electricians come out to bid upgrading my service...
frank_diy
© 2015 Houzz Inc. Houzz® The new way to design your home™