Subpanel wired with common neutral and ground

whispertooJune 19, 2013

This is a 100A subpanel used for A/C, electric heat, and 2 other 20 A circuits. Service entrance cable was used and the bare aluminum is connected to the isolated neutral bus- and of course there is no ground. I know this has to be fixed, but running the proper new cable will be very difficult- But a single wire could be more easily managed.
My question- Is it permissible to run an insulated neutral wire outside and alongside the SE cable to the isolated bus and move the twisted uninsulated alum to a new ground bus properly bonded to the box?
If no- then how about a 10/2 with all 3 conductors twisted together to provide the missing neutral?

Thank you for reporting this comment. Undo
Ron Natalie

No and HELL NO.

    Bookmark   June 20, 2013 at 10:38AM
Thank you for reporting this comment. Undo
bus_driver

One simple correction is to use Type SER cable to completely replace the existing sub-panel feed.

    Bookmark   June 20, 2013 at 12:09PM
Thank you for reporting this comment. Undo
whispertoo

OK- Thanks for these replies.
One last question.
If I remove all 120V breakers and just devote this subpanel to 240 -2P loads (no neutral and thus no neutral current) does it still need a neutral wire from the main to meet code?

Here is a pic- obviously not done by a good electrician.

    Bookmark   June 21, 2013 at 6:43AM
Thank you for reporting this comment. Undo
Ron Natalie

WHOH Not done by a good electrician? Not done by an electrician at all. In addition to the improper grounding, it's only a matter of time until that piece of NM running through the naked hole wears through and electrifies that panel (hopefully tripping a breaker in the process but given the dumbass grounding procedure, there's no indication that it will happen before killing somebody).

I fear that if I had more of that picture, I'd find more dangerous, stupid, and otherwise illegal stuff going on.

Get thee to a qualified person!

    Bookmark   June 21, 2013 at 11:57AM
Thank you for reporting this comment. Undo
whispertoo

Yes ronnatalie, That's what I meant-
There is one other 20A cable coming in the same way lower down in the box.
Can anyone give an opinion about my last question?

    Bookmark   June 24, 2013 at 1:39PM
Thank you for reporting this comment. Undo
Ron Natalie

If there are no 120V (or other loads requiring a neutral) you MIGHT get away with it, but frankly I suspect an inspector will give you a hard time on a panel wired as such because nothing stops some unsuspecting person from adding such a load later not realizing the goofball cob job this is.

    Bookmark   June 25, 2013 at 12:40PM
Thank you for reporting this comment. Undo
whispertoo

We removed the subpanel and used the SE cable with a
60 A disconnect at the A/C location to serve the AC with 240V.
Changed breaker from 100A to 60 A in the main panel.
Other circuits were rewired to the main panel.
Looks better now.

Thanks to all who replied.

    Bookmark   July 21, 2013 at 2:11PM
Sign Up to comment
More Discussions
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Where to find power connectors for the LED under cabinet lights?
I bought a set of the GE/Jasco LED under cabinet lights...
flyingkite
Doorbell goes off by itself.
Can anyone tell me why this would happen? It's a wired...
stu2900
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™