Circuit Breaker Tripping

gellerJune 13, 2013

We have an older house with a mixture of wiring from BX to NM installed at various times. We have 200 A service with a nearly full breaker panel, and a partly finished basement so it's not easy to trace wires. Up 'til now, we have not had any electrical problems in the 12 years we've lived in the house.

Today, during an electrical storm, a breaker tripped, and it trips almost immediately or a few seconds after resetting.

The breaker supplies (as nearly as I can tell) two light fixtures in the finished basement ceiling, each with their own switch, and two outlets on the first floor of the house. It trips even with nothing plugged into the outlets and the light switches off. Nothing else is amiss in all of the other circuits.

When it trips, I do hear a popping sound above the basement finished ceiling (not in proximity to the lights or the outlets), and if it doesn't trip immediately, I can faintly detect an arcing smell. Other than taking down the ceiling, is there an easy way to troubleshoot what the likely cause is? This is an older circuit likely to have BX.

The electrical work looks all very professional so I'd be surprised if there were a hidden splice or box above the ceiling, but I suppose they could have put the ceiling over an existing box. I also checked that it does not supply any outside outlets.

Thank you for reporting this comment. Undo
randy427

If you are reasonably sure that there is no forgotten outlet or other device in this circuit on the first floor above the sound of arcing and sparking, then it sounds like you'll need to open up one or more inspection holes in the ceiling.
Considering that this may be the result of a lightning strike, it could involve more than one circuit, only one of which is now tripping a breaker, so it's not something to delay addressing.

    Bookmark   June 14, 2013 at 7:17AM
Thank you for reporting this comment. Undo
geller

I am 99% certain that there are no other devices on the circuit, as I went all around the house with a tester. I was figuring that we'd have to open up the ceiling, fixing of which will be more expensive than the electrical work. The ceiling boxes are all very tight with the drywall, and the joists are perpendicular to the unfinished area, so there's no room for poking around, though it might be possible to open a hole that's covered by the surface fixture and peek around. But this seems like something for a professional who has the right tools and experience.

    Bookmark   June 14, 2013 at 10:43AM
Thank you for reporting this comment. Undo
brickeyee

You can check inside the fixtures, and at junction boxes you have access to.

these are often common places for failures to occur.

An actual failure in the branch circuit cables is not as common, but if there is a weak spot in old insulation even a nearby lightning strike can produce enough further damage to trip a breaker (and ruin a section of cable by producing a permanently damaged spot in the insulation).

We used to use 'meggers' (mega volt meters) to produce high voltage to trouble shoot these types of problems, but most modern digital meters in resistance mode on a turned off and disconnected circuit are more than adequate for checking insulation for weak spot.

This post was edited by brickeyee on Fri, Jun 14, 13 at 16:34

    Bookmark   June 14, 2013 at 11:25AM
Thank you for reporting this comment. Undo
ionized_gw

It might be easier to re do the circuit than to fix the old one. You might try to figure out what order the outlets and lights are in. For the lights, remember that the main circuit can go to the boxes with loops to the lights or can run to the lights with loops for the switches. If you are lucky, you might find that the problem is right before the last device in the circuit and you can get along without it.

    Bookmark   June 14, 2013 at 2:14PM
Thank you for reporting this comment. Undo
randy427

I'd look first where the sizzleing, popping and fumes are coming from. By opening up the known junction boxes, you should be able to visually detect if the fault is there.
An inspection hole can be covered, at least temporarily, by a prefab plastic access panel that can be found at a builders supply store (or electrical supply or plumber's supply).

    Bookmark   June 14, 2013 at 3:25PM
Thank you for reporting this comment. Undo
btharmy

"I was figuring that we'd have to open up the ceiling, fixing of which will be more expensive than the electrical work."

Wow! You either have a very expensive finisher/painter or a very cheap electrician. I have had customers say, "Run a new circuit, I don't want to have to patch a hole." Ok, If I am $100+ per hour. How expensive is their painter?

    Bookmark   June 14, 2013 at 4:55PM
Thank you for reporting this comment. Undo
geller

Thanks, all. I will take home a meter and measure resistance. I disconnected one of the two fixtures and the breaker still tripped. I can easily disconnect the other and the outlets and do the same. Unfortunately, we do need both the outlets and the lights, so there is no shortcut here.

    Bookmark   June 14, 2013 at 6:14PM
Thank you for reporting this comment. Undo
brickeyee

The is one of those things tat hiring someone fr is painful expensive, but if you can DIY can save a lot of money.

One 'trick' to checking permanent wiring to use an extension cord to 'stretch' meter leads.

You can plug the cord into a receptacle ad then measure the resistance at the far end between another junction with the permanent wring included.

It ranks up there with using an extension cord to make a ground available for voltage measurements on 'hot' circuits in older work with no wired ground.

    Bookmark   June 15, 2013 at 8:59AM
Thank you for reporting this comment. Undo
geller

Our electrician called to check on the issue, and he thought the most likely explanation is a bad breaker. He suggested that 1) I disconnect the wire from the breaker and measure resistance of the circuit. (He knows me well and that I have an EE degree). If it's low, then there is a short, Extension cord is a good idea, though the outlets are readily accessible. If resistance is OK, he suggested that I then swap breakers with another circuit of the same rating. If the old breaker trips, it's the breaker, while if the new breaker trips, it's the circuit. Fortunately, these circuits are not essential for our daily life, so I can take my time.

    Bookmark   June 15, 2013 at 11:01AM
Thank you for reporting this comment. Undo
bus_driver

For situations such as the one you describe, I use a pigtail socket with an incandescent lamp, 15 watt is smaller and not as easily broken as is the 60. Remove the circuit conductor from the breaker, place one of the pigtail leads to the breaker and wire nut the other to the circuit conductor. Thus the incandescent lamp is now in series with the circuit. So long as there is a load or short circuit, the lamp will be lighted. When the problem is located (working it hot) the lamp will go off. This allows testing with very low current, limiting potential damage to any conductors. But remember that the circuit is energized and as potentially lethal as any other circuit on the premises.

    Bookmark   June 15, 2013 at 1:31PM
Thank you for reporting this comment. Undo
geller

Thanks to all. This morning, 5 days after the breaker tripped, I disconnected the circuit from the breaker and it did not trip. I then put in the pigtail, turned on the breaker, and the bulb did not glow. I put a bulb in one of the fixtures and turned it on, and both bulbs glowed. I then reconnected the circuit and all outlets and lights are working.

My diagnosis is that something got wet and shorted, and now dried out. If so, this will happen again in the future. Is there another potential explanation? Should I replace the circuit wiring anyway (at least at the panel, it's BX)?

    Bookmark   June 16, 2013 at 11:55AM
Thank you for reporting this comment. Undo
brickeyee

That is actually a very possible scenario with older AC cable with cloth covered rubber insulation.

Find the wource of the water.

Water in walls a ceilings enough to soak into older AC cable is going to do a LOT of other damage if not stopped.

The wet cable will be the least of your problems if you have a water issue (and yes, just replace it with a section of NM).

This post was edited by brickeyee on Sun, Jun 16, 13 at 15:51

    Bookmark   June 16, 2013 at 12:35PM
Sign Up to comment
More Discussions
Want to save shower recessed light
I have 2 matching recessed lights in my bathroom. One...
africanboy
Troubleshooting Kohler 12RES Problem
I have a Kohler 12RES generator with an RDT 100 Amp...
sniffdog
Grounding Service panel 200amp
Is the new NEC saying to no longer run # 4 copper wire...
36066
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Sponsored Products
Museum of New Mexico Valiant Bronze San Gabriel Table Lamp
$419.99 | Bellacor
6 in. Fluorescent New Construction IC Airtigh
PLFixtures
Progress Lighting Brushed Nickel Track Accessory, Flex Connector P8736-09
$39.60 | Home Depot
DW 3528 Single Row LED Strip Light 240/m 10mm wide Foot
EnvironmentalLights.com
Circuitous Iron 5 Lights Wall Lighting With Clock
ParrotUncle
Progress Lighting Track Lighting Alpha Trak White Track Lighting Connector
$22.41 | Home Depot
Inglenook Valiant Bronze Dome Pendant
$269.99 | Bellacor
Elenco Snap Circuits Green - SCG-125
$74.95 | Hayneedle
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™