Am I going to have a problem with voltage drop or heat?

jca1June 2, 2011

Hi, first post in a while, need some help from any electricians on board.

I have an outdoor building 12x12. It has been converted to an outdoor kitchen. There is a sub panel fed by a 60amp breaker and 6AWG copper THHW conductors(4) in PVC conduit from my main panel in our house, 160' away. Now all of a sudden I have the following loads:

8000 BTU window AC (new unit) 7amps

1 stand mixers 2.7 amps

one small drink cooler/fridge thing 2.5amps

a small microwave that would only be used on occasion

and now a 16amp electric oven (240Vac)

For a total of approx 40 amps not figuring any LRC on the AC and fridge.

Best I can tell voltage drop for 6AWG at 60 amps for that distance would be a shade over 3%

Is this going to work OK?

Thank you for reporting this comment. Undo
Ron Natalie

THHW will be illegal unless it was also rated THWN or something else approved for wet locations, but most of the stuff out there these days is.

Your voltage drop estimations sound reasonable. Even at 60 it would be OK, you'll have less drop owing to the fact that your actual current flowing appears to be less than 30 most of the time (assuming your 120V loads are distributed across both legs).

The new building will need it's own grounding system (rods).

    Bookmark   June 3, 2011 at 6:29AM
Thank you for reporting this comment. Undo
jca1

Sorry, the conductors are THWN wet rated, I typed it wrong.

    Bookmark   June 3, 2011 at 6:43AM
Thank you for reporting this comment. Undo
jca1

Just a follow-up.

I checked amp's at the Sub-panel and with everything running and had right at 20amps per 120VAC leg. Checked voltage at AC recep. with AC off: 120VAC; with AC on and compressor running 118VAC.

    Bookmark   June 4, 2011 at 1:06PM
Sign Up to comment
More Discussions
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™