nm wire to conduit

satlt4uJune 24, 2010

can i run nm wire into metal coduit junction boxes and thru new studed walls or does all new wiring have to run in conduit?

Thank you for reporting this comment. Undo
brickeyee

The NEC allows NM, but some local codes (Chicago being a notorious example) require all wiring to be in conduit.

    Bookmark   June 24, 2010 at 6:55PM
Thank you for reporting this comment. Undo
2ajsmama

Not to hijack, but I have similar question. We want to install exterior GFCIs on our garage (forgot during build, we have one on back of house and 2 on porch but they're too far for charging battery on tractor, etc.). Have 20A circuit for interior garage receptacles and 1 dedicated for freezer.

Electrician did not use conduit - ran all the 12/2 (and 14/2 for lights) up in trusses, then down through holes along studs where (plastic) outlets are located. I want to pull off one outlet in back of garage, would be easy to take out a couple of staples, pull wire up, drill new hole and run it down a few feet over for new exterior box. Then to save wire I was hoping to run either straight through a couple of studs (as is done in interior house wiring) or *down*, put the holes low in studs, and then up a couple of feet to new box. If I ran straight across I would put in conduit. If I ran down to sill plate, would it need to be in conduit? Or, do I have to run *up* and over like all the other wiring in garage?

Walls are just studded out, no insulation or drywall (except shared wall with house). We may finish them at some point.

    Bookmark   June 25, 2010 at 8:44AM
Thank you for reporting this comment. Undo
brickeyee

" If I ran straight across I would put in conduit. If I ran down to sill plate, would it need to be in conduit? Or, do I have to run *up* and over like all the other wiring in garage?"

Ask your AHJ.

It all comes down to the interpretation of 'subject to physical damage' in the NEC.

There are some AHJs that make a big deal of exposed NM that is in reach from people, tools, stored material, etc. while other accept that NM on the side of a stud or running in bored holes through studs (stay 1.25 in from the faces) is acceptable.

Running higher on the wall does put the cable in a location less likely to be damaged, but it is stil the AHJs call.

    Bookmark   June 25, 2010 at 8:53AM
Thank you for reporting this comment. Undo
2ajsmama

Well, our electrician thought running along the side of studs was fine. Frankly, I don't think the AHJ even looked at it. He left, we've got a new inspector in town, I don't know if I want him to look at it b/c I don't know what he's going to think of original work.

I figured running 2-2.5ft off the floor might be subject to damage (esp. since DH likes to store tools in back of garage, most hanging on hooks on outside of studs but he stuck some strapping across and sticks long-handled tools in there - I would have to get him to change that to put new outlet in the location I want near the back corner - just found hacksaws hanging on a nail right near drip loop for floodlight!). Wasn't sure about sill plate or toward the back of the cavity (put a "plate", even if it's just plywood or a 2x6, over it so broom handle doesn't sit on wire?).

    Bookmark   June 25, 2010 at 9:59AM
Sign Up to comment
More Discussions
Light boxes on/in 6X8 timber floor joists for log home
Just trying to figure how to wire a couple light fixtures/chandelier...
yota_85
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
ceiling fan, fan works but lights do not
I have 2 kids and one threw a toy that hit one of the...
katy_bug
Looking for Ideas For Lighting at base of 300' long driveway
Sorry for the "picture through the screen"...
dixieman