220 wiring, alluminum to copper??

mattdinkc10June 8, 2010

helping my parents with a project, and will hire an electrician, but I want to understand.... house has alluminum wiring. They are replacing a wall oven/M-w single unit with 2 sepreate appliances. I need to add a new dediacted 110 for the MW, can I run new copper in the old panel? what is the solution? the oven is hard wired, can I join old 220 alluminum to new copper (using proper purple caps)? Thanks in advance

Thank you for reporting this comment. Undo
petey_racer

Depends on what "old 220 aluminum" is. "220" is no indication of wire or circuit size.

Sure, you can run any new circuit you want to an older panel. The panel does not care. In fact, the only restrictions would be for aluminum. Some terminations are not rated for AL.

    Bookmark   June 8, 2010 at 9:39PM
Thank you for reporting this comment. Undo
mattdinkc10

Thanks. I was making assumption that the original oven was hard wired with alluminum since the entire house has al. wiring. I will be tearing out the old oven next weekend to confirm what is back there.

    Bookmark   June 8, 2010 at 10:18PM
Thank you for reporting this comment. Undo
brickeyee

There is no problem or issue with larger size stranded aluminum wiring.

The problem is with solid aluminum wire for 15 A and 20 A branch circuits.

The softness (lack of temper) required to make the wire flexible for installation makes it soft enough to deform under connections when it heats up (even a little) and this makes the connections become loose.

This creates more heat, deformation, and can lead to arcing and fires.

    Bookmark   June 9, 2010 at 9:24AM
Thank you for reporting this comment. Undo
mattdinkc10

Thanks brick, always appreciate your feedback thru out the forum. as in allum to copper on 15 amp circuit, is it done the same way with purple caps and inhibitor on larger sizes?

    Bookmark   June 9, 2010 at 5:26PM
Thank you for reporting this comment. Undo
brickeyee

The Copalum crimp connections are much more reliable than the corrosion inhibitor filled purple caps.

The purple caps are better than standard wire nuts.
The problem appears to be that to function the spring in the purple wire nut becomes a part of the current path and is simply not sized for that function.

If the Al conductors are well cleaned to bare aluminum and the purple nuts installed immediately (Aluminum oxide starts forming instantly on the clean surface) with solid contact between the conductors the inhibitor does slow the oxide growth, but it does not last forever.

The Copalum crimps require training before the manufacturers will sell them to anyone.

The problem does not occur with larger stranded aluminum conductors since they are suitable tempered. The bend radius is already large, based on the total conductor size, so the flexibility needed for single solid wires is not required.

    Bookmark   June 10, 2010 at 9:18AM
Thank you for reporting this comment. Undo
mattdinkc10

Thanks. screw it, not messin' with the alluminum, going to pull new copper and try to talk my folks in to re wiring the entire house

    Bookmark   June 10, 2010 at 1:00PM
Thank you for reporting this comment. Undo
brickeyee

Replacing all the smaller general purpise branch circuits is a good idea.

It is the larger ones (central air, electric heat, water heaters, stoves, dryers. etc.) that should be fine if they are stranded aluminum.

Just as in the past large size copper wire is painfully expensive compared to (even larger for the same ampacity) stranded aluminum.

    Bookmark   June 10, 2010 at 3:55PM
Sign Up to comment
More Discussions
Outdoor subpanel as AC disconnect
Can we use an outdoor subpanel as an AC disconnect?...
ylmzm
Can I electrify battery-operated lights?
Hi all. Is there a way to electrify a battery operated...
eam44
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
Confused & need help please
I know just about zero when it comes to electricity....
bicyclegirl1
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Sponsored Products
One of a Kind Gabbeh Collection 6x9 Green Chobi Hand Knotted Wool Area Rug H6889
BH Sun Inc
Heaven & Earth I Table Lamp by Fire Farm
$291.60 | Lumens
Weatherproof High Power LED Flexible Light Strip - WFLS-x
Super Bright LEDs
Scuba Wine Caddy
$99.00 | FRONTGATE
White Lucille Counter-Height Dining Set
$179.99 | zulily
WW 3528 Single Row LED Strip Light 120/m 10mm wide 5m Reel
EnvironmentalLights.com
Hudson Valley Lighting | Logan Wall Sconce
$278.00 | YLighting
Harmony Face Cloth - COPPER (ORANGE)
$9.00 | Horchow
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™