What's the best way to wire?

footwedgeJune 27, 2011

The kitchen cabinets are being installed as I type. The installer mentioned surface mounting the receptacle box for the microwave, garbage disposal and dishwasher in lieu of my plan of recessing them. I like his plan better.

I will also be adding one in the lazy susan for the tv.

I prefer the shallow surface mount box especially for the lazy susan location but I guess I could get by with using a standard box for the other locations. Each location will require a minimum of 11.25 cu. in. ( 3 no. 12 and 1 receptacle).

What's the best way to handle this?

Thank you for reporting this comment. Undo
brickeyee

Where will the microwave be sitting?
If the receptacle is behind the microwave it will not be able to fit as far back on the counter or shelf.

Disposal and DW receptacles are normally under the sink and all you give up is a few inches up off the bottom of the cabinet on the wall.

I usually hard-wire both so there is no need for a receptacle.

    Bookmark   June 30, 2011 at 4:09PM
Thank you for reporting this comment. Undo
footwedge

I put the micro outlet in the cabinet above and I just wired a metal jb using the romex cable connector and a little bit of flex and laid the receptacle on the cabinet bottom. This is the uppermost cabinet that is 8' tall and 2' deep.

I decided to go ahead an recess the other 3 locations. It will just look better.

Was told the code no longer allows direct wire, must use a receptacle.

    Bookmark   June 30, 2011 at 11:14PM
Thank you for reporting this comment. Undo
brickeyee

"Was told the code no longer allows direct wire, must use a receptacle."

What code?

Ask for a code citation.

Cords are permitted but not required under the NEC.

    Bookmark   July 2, 2011 at 8:29PM
Thank you for reporting this comment. Undo
footwedge

Must be a local requirement if not required by the NEC.

    Bookmark   July 7, 2011 at 7:46PM
Thank you for reporting this comment. Undo
brickeyee

"Must be a local requirement if not required by the NEC."

Who made the claim?

You would be surprised how often 'rules' disappear when you ask the AHJ for an actual code citation.

    Bookmark   July 8, 2011 at 9:19AM
Sign Up to comment
More Discussions
Inspection Report
Had a gorgeous 1909 house inspected yesterday and don't...
cmae17
Same circuit for AC air handler and whole-house fan?
Hi, I've got a furnace/air handler in my attic. I was...
elofgren
Want to save shower recessed light
I have 2 matching recessed lights in my bathroom. One...
africanboy
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Bath fan/light combo
Attached is wiring diagram of masterbath (I hope I...
jaspol
Sponsored Products
Mother Earth Sculpture - GOLD
$1,035.00 | Horchow
Meilana Distressed Bronze Table Lamp Set of 2
Lamps Plus
Wire Bath Basket -13
TheBathOutlet
Fifth Avenue Winter Gold One-Light Lantern Pendant
$278.00 | Bellacor
Chooty & Co. Anderson Zippered Beads Foot Stool - Red - BP13K2110
$42.99 | Hayneedle
Joplin Pendant
Lightology
1 Light Recessed Brick Light
$48.60 | PLFixtures
Beach Wood Succulent Garden
$49.99 | Dot & Bo
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™