Homeline Surgebreaker Question

gardug0213June 16, 2012

I have a Square D Homeline 200A panel. I just installed an in-panel Homeline Surgebreaker [HOM2175SB] on the top right 2 breaker positions [#2 & #4] with the neutral at the top most position on the nautral bar located on the right side of the panel. My question is, this panel has 2 neutral bars [left and right side]. Would there be a need for 2 Surgebreakers [one on each neutral bar], or is the single Surgebreaker giving me adequate coverage on circuits attached to both neutral bars.

Thank you for reporting this comment. Undo
Ron Natalie

No. One will do it. The neutral/ground bars are pretty strongly bonded together out of necessity. The instructions for the device do recommend keeping the connecting wire as short as possible without any sharp bends.

    Bookmark   June 18, 2012 at 8:18AM