Underground wiring

don_1_2006June 14, 2011

Is there an equivalent to 14/2 UF that is stranded? If so how is it designated?

Thank you for reporting this comment. Undo
mstr_electrician

No there isnt an equivalent thats stranded. What can be done is install non-metallic rigid conduit(electrical pvc) in the ground at the required depth(24" from grade to the top of the conduit meets all requirements) and use THHN instead of a sheathed cable. Both ends of the conduit must be terminated into a box such as a Bell box.

    Bookmark   June 14, 2011 at 1:55PM
Thank you for reporting this comment. Undo
don_1_2006

Okay thanks.

    Bookmark   June 14, 2011 at 2:09PM
Thank you for reporting this comment. Undo
kurto

Given that you specified UF, it implies a wet location, and therefore you need THWN. Most wire is rated both THHN and THWN, but it always pays to check.

    Bookmark   June 14, 2011 at 2:41PM