Should I splice or replace underground

skinnycatJune 7, 2010

electric service? Yday I dug through 2" pvc conduit, and the 4AWG thhn individual conductors within. The conduit contains 2 phase and 1 neutral, powered through a 60 amp breaker, feeding a breaker panel in a workshop.

Conduit is 18" below ground, has been in continuous service for 18 years. The break is in the middle of a 90' run. Counter man at electrical supply suggested installing a water proof box (12" by 12" by 6") and splicing.

So my decision is whether to splice, or pull new wire. Heck, I suppose I could install sweep bends to bring the j box up to surface level, or even slightly above ground and mount it flush w the sidewalk that it runs next to, and help keep inside of box dry.

Thank you for reporting this comment. Undo
randy427

I'd stay away from underground splices, even if they can be done legally. For the above ground box you'll need more conductor length so you'll either need to replace half of the entire length or use two j-boxes several feet apart with new conductors between.
IMHO, the best way is the 'right' way which is to replace the entire run.

    Bookmark   June 7, 2010 at 12:19PM
Sign Up to comment
More Discussions
Same circuit for AC air handler and whole-house fan?
Hi, I've got a furnace/air handler in my attic. I was...
elofgren
Light/Switch wiring
Here is the scenario. Have a kitchen light that needs...
wgl3333
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Power to shed
Looking to run one 20 amp circuit to my shed and I'm...
ohio45424
Badly done multi-wire circuits (previous owner strikes again..)
I bought a 1940-ish house last year, for which the...
quahog
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™