I'm painting my dining room and noticed that the outlets in this 20A circuit were somehow backstabbed. The wiring itself is 12 gauge, but the outlets have 14AWG pigtails, backstabbed, and connected to the 12AWG conductors in each box.

Is this in compliance with NEC? I know that 20A requires 12AWG, but does this apply to the pigtails also?

Thank you for reporting this comment. Undo
dennisgli

Are the outlets 20amp or 15amp?

    Bookmark   June 5, 2011 at 11:32AM
Thank you for reporting this comment. Undo
petey_racer

Yes it applies to pigtails. NO, it is NOT allowed.

It does NOT matter if the receptacles are 15 or 20A. It is on a 20A circuit.

    Bookmark   June 5, 2011 at 12:46PM
Thank you for reporting this comment. Undo
tom418

Thank you, Petey and Dennis.

I kind of figured it wasn't allowed. BTW, these are 15A with 20 AMP "pass through" outlets.

It's par for the course, as the circuit continues into the adjoining living room. I also have a small applicance kitchen circuit that found itself feeding an outdoor outlet too(fixed years ago, by me). BTW house was built in 1996.

    Bookmark   June 5, 2011 at 1:23PM
Thank you for reporting this comment. Undo
brickeyee

"BTW, these are 15A with 20 AMP "pass through" outlets. "

The pass through requirements oif 20 amps was established at the same time as the NEC allowance of 15 amp OR 20 amp receptacles on 20 amp circuits (as long as more than one outlet is on the circuit).

The use of back stabs for #12 wire was very short lived.
Reliability was so bad the receptacles were changed to not accept #12 wire by reducing the hole for back-stabbing to only accept #14 wire.

Whomever used the #14 pigtails was a real hack.
#14 wire is NOT allowed on a 20 amp general use circuit, and they used it to get around the change to the receptacles.

You can just move the wires to the screws and eliminate the pigtails.

    Bookmark   June 6, 2011 at 10:10AM
Thank you for reporting this comment. Undo
mstr_electrician

According to NEC Article 210.24, using a #14 wire on a 20 amp circuit as taps (pigtails) is allowed. I don't agree with this method but it is not a violation of the NEC.

    Bookmark   June 7, 2011 at 8:31AM
Thank you for reporting this comment. Undo
sofaspud

I find it interesting that it would be allowed, since it would set up a circumstance where someone could install a 20 amp outlet with #14 wire, but then again, there's nothing preventing a homeowner from installing a 20 amp outlet on a circuit that's 15 amp all the way to the panel. Anyone trying to do the right thing might look at the breaker, see that it's a 20, and feel perfectly safe installing a 20 amp outlet, not knowing the pigtails are #14.

    Bookmark   June 8, 2011 at 11:31AM
Thank you for reporting this comment. Undo
dennisgli

Now I'm confused.

According to NEC Article 210.24, using a #14 wire on a 20 amp circuit as taps (pigtails) is allowed. I don't agree with this method but it is not a violation of the NEC.

So this is OK even if the tap is feeding a 20amp receptacle?

    Bookmark   June 11, 2011 at 11:42AM
Thank you for reporting this comment. Undo
mstr_electrician

Yes Dennis, it is ok the pigtails are #14 on the 20 amp circuit according to the NEC.

    Bookmark   June 14, 2011 at 1:46PM
Sign Up to comment
More Discussions
electrical outlet distance to radiator
how far from a radiator should a wall electrical outlet...
amsayan
Help with 240V 50A location
I'm trying to do a challenging kitchen layout. I will...
12crumbles
Replacing fan speed dial back to standard toggle?
I am removing a ceiling fan and replacing it with a...
onkyokoi
Need help Replacing old dimmer that used only 2 wires in a three way
I need advice as to which wire to connect to which...
txmat
new wiring project
I have a water damaged room I will soon be renovating....
CharlesInVT
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™