I've just bought an apartment and am renovating it. Just started on the electrical wiring and have a question.

At the main fuse box, I'm receiving 3 wires that enter the apartment - line (220AC), neutral and ground (presumably connected to the grounding installation of the entire building). There is a main GFCI breaker with the rating of 40/0.5A and a separate GFCI breaker for the bathroom with the rating of 25/0.03A. The apartment piping has been replaced and is now plastic. The bathtub i also plastic.

My question is - do I have to ground the metal faucets that connect on the end of plastic piping? Can these anyhow turn out "hot" since they are not connected to metal piping? For instance if a lightning strikes near the building (or onto the building itself) can a dangerous charge accumulate in the faucet and then discharge itself when I (or someone else) hold it?

The second question relates to the following hypothetical situation:

Let's say the plastic bathtub is filled with water, connected to the plastic piping and a person is inside it. The same person has a very bad habit of operating electrical equipment while taking a bath (stereo, hairdryer, etc...). What happens if a hairdryer falls in the water (remember the piping and the bathtub are plastic)? My bet is that the breaker will trip, but the GFCI will not since none of the current "escapes" to the ground (bathtub is basically isolated right?). Will the human inside the bathtub be in danger during this? If so how can one make the GFCI trip? My idea was to somehow ground the bathtub so at least some of the current would escape to the ground and that could only be done by grounding the metal ring at the drain at the bottom of the bathtub (the drainage piping that continues is also plastic). Would this work? Or do I worry too much and no harm can happen since the piping is plastic? :)

Thank you for reporting this comment. Undo
manhattan42

"do I have to ground the metal faucets that connect on the end of plastic piping? Can these anyhow turn out "hot" since they are not connected to metal piping?"

No and no.

"What happens if a hairdryer falls in the water (remember the piping and the bathtub are plastic)? My bet is that the breaker will trip, but the GFCI will not since none of the current "escapes" to the ground (bathtub is basically isolated right?)."

Not correct.

The GFCI will trip. GFCIs operate by sensing a difference between the current coming into the receptacle and the current leaving the receptacle. The GFCI will trip when this difference is about 6 millivolts.

If you are on a grounded electrical system, the equipment grounding conductor of the bathroom circuit grounds the GFCI back to the main panel.

"Or do I worry too much and no harm can happen since the piping is plastic? :)"

You worry too much because you have no idea how GFCIs and how residential wiring works.

Relax.

    Bookmark   June 27, 2010 at 6:59AM
Thank you for reporting this comment. Undo
hendricus

At the main fuse box, I'm receiving 3 wires that enter the apartment - line (220AC), neutral and ground

Not correct. You have two hot lines at 110/120 each and a combination neutral and ground.

    Bookmark   June 27, 2010 at 8:17AM
Thank you for reporting this comment. Undo
brickeyee

"What happens if a hairdryer falls in the water (remember the piping and the bathtub are plastic)? My bet is that the breaker will trip, but the GFCI will not since none of the current "escapes" to the ground (bathtub is basically isolated right?)."

Not correct.

The GFCI will trip. GFCIs operate by sensing a difference between the current coming into the receptacle and the current leaving the receptacle. The GFCI will trip when this difference is about 6 millivolts.

Maybe nothing since without a grounding (3-wire) plug or some pother path to ground the current will NOT be unbalanced (hot not matching neutral through LOAD side terminals).

Current is measured in amps (amperes) not volts (or millivolts).

To trip GFCI there MUST be another path for the current to take.

No path, no current, no GFCI trip.

If you then touched the water and provided another path (possible not not guaranteed) the GFCI would trip.

That path must be present and be low enough impedance to allow ~6 milliamps to flow in the circuit with the voltage available.

    Bookmark   June 27, 2010 at 10:22AM
Thank you for reporting this comment. Undo
abnorm

Posting from Croatia !

    Bookmark   June 27, 2010 at 3:02PM
Thank you for reporting this comment. Undo
brickeyee

GFCIO devices work the same everywhere.

    Bookmark   June 27, 2010 at 8:25PM
Thank you for reporting this comment. Undo
manhattan42

"Current is measured in amps (amperes) not volts (or millivolts)."

That is correct. Current is measured in milliamps not millvolts for GFCI trip currents. Sorry for mis-speaking.

"To trip GFCI there MUST be another path for the current to take.

No path, no current, no GFCI trip."

That is not correct. There is no need for an equipment grounding conductor to be present for a GFCI receptacle to trip.

GFCI receptacles trip by sensing a current imbalance between the hot and neutral. This imbalance causes a magnetic field to form in a metal ring through which these conductors pass. It is this magnetic field that causes the breaker to trip in the GFCI device...not the presence or absence of an equipment grounding conductor.

This is why GFCI receptacles can be used to replace ungrounded receptacles on ungrounded circuits.

See Art 406(D)(E)(3)(a) which says when replacing receptacles when no equipment grounding conductor is present that "Grounding-type receptacles supplied through
the ground-fault circuit interrupter shall be marked 'GFCI Protected' and 'No Equipment Ground'."

It is not necessary for an equipment grounding conductor to be present for a GFCI to work.

    Bookmark   June 28, 2010 at 6:39AM
Thank you for reporting this comment. Undo
brickeyee

"To trip GFCI there MUST be another path for the current to take.
No path, no current, no GFCI trip."
"That is not correct. There is no need for an equipment grounding conductor to be present for a GFCI receptacle to trip."

I did not say a "equipment grounding conductor" was required.
I said "there MUST be another path for the current to take."
Without another path all the current will remain on the neutral and there can be no imbalance.
The path could be through metallic piping than is bonded to ground, or any other path that will allow 6 milli-amps to flow with the available voltage, but there MUST be another path for this current to take.

If you grab the hot and neutral of a GFCI protected circuit you can be killed if there is not another path that unbalances the current the GFCI is measuring.

Current does not Âpile up or Âcollect but flows in complete circuits.
The common demo of placing a drop light into a plastic bucket of water ONLY works if the grounding conductor is present in the drop light.
Otherwise there is NOT a path to unbalance the hot-neutral current.
The light stays lit very nicely.
If you touch the water and provide a path the GFCI will trip, but not until that path is created.

" is not necessary for an equipment grounding conductor to be present for a GFCI to work. "

Very true.
A grounding conductor is not required, but ANOTHER CONDUCTING PATH MUST BE PRESENT.

It is painfully easy to have the path, but it must be present.

A plug in GFCI tester does not work on GFCI devices without a grounding conductor.
The tester shunts the current to the ground connection to unbalance the hot-neutral current.
You can push the tester button till the cows come home and nothing happens.
No ground connection, no unbalance, no trip.

This is rather basic electrical stuff.
Without a closed circuit current does not flow.

    Bookmark   June 28, 2010 at 8:57AM
Sign Up to comment
More Discussions
Does a refrigerator need to be on a separate circuit?
Does a refrigerator need to be on a separate circuit?...
rontero
Need help with a rocker switch
I need to replace it in our SunHeat radiant room heater....
bold_as_love
Multiple Fluorescent Ballasts in one light fixture
Hello GardenWeb. I'm not new here, but couldn't log...
MikeM21
Well this sucks
Just when you thought the idiot popup ads in the gardenweb...
Ron Natalie
Spa Capacitor question
My spa is wired for 220v. The pump motor is rated for...
pugmark
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™