covering of outdoor wires frayed

snuffypotsMay 8, 2012

The covering of the wires that lead into my house are frayed but I have been told the wires are in good shape. It is only the covering that is bad. I would like to get the wires recovered. Is that possible? Also I do not know the terms to use when talking to an electrician about this problem. I hope someone can help me with this dilemma. Thanks.

Here is a link that might be useful: picture of wires

Thank you for reporting this comment. Undo
kurto

If the wires are between the pole and your meter, it's frequently the responsibility of the power company to replace them (varies somewhat depending on the area). You can always call the POCO and ask them who is responsible. If the wire that's frayed is between the meter and your circuit breaker/fuse box, it's called a service entrance cable, and any qualified electrician will be able to help you.

    Bookmark   May 8, 2012 at 9:58PM
Thank you for reporting this comment. Undo
petey_racer

NO wire or cable like this can be "recovered" if frayed. It MUST be replaced.

The overhead drop from the pole to the house is the POCO's responsibility.
The wires from the connection at the top, down to the meter, and from the meter to the panel, are typically customer responsibility.

    Bookmark   May 8, 2012 at 10:09PM
Thank you for reporting this comment. Undo
brickeyee

"The wires from the connection at the top, down to the meter, and from the meter to the panel, are typically customer responsibility. "

Very location dependent.

In Virginia the POCO is responsible to the top of the meter box for residential service (or the bottom for buried service).

    Bookmark   May 9, 2012 at 12:35PM
Thank you for reporting this comment. Undo
petey_racer

I understand that Brick, but I think that is a very rare case these days, which is why I said typically.

It is safe to say, in "most" places the POCO stops at the taps.

    Bookmark   May 9, 2012 at 7:23PM
Thank you for reporting this comment. Undo
brickeyee

One of the reasons the POCO's keep control of lines to the meter is because the NEC does not actually cover them since they are distribution wiring.

While there are rules for weather heads and drops, they are not applicable to these items since they are technically POCO distribution equipment.

    Bookmark   May 10, 2012 at 10:12AM
Thank you for reporting this comment. Undo
weedmeister

Snuffy: it would be nice to see where this wire goes in both directions. That is, some more pictures.

    Bookmark   May 10, 2012 at 4:55PM
Thank you for reporting this comment. Undo
bus_driver

That is an SE cable. The outer covering has weathered away. It does not provide electrical insulating properties and never did. It is probably at least 50 years old. While new installations here require the property owner to supply and pay for everything including and after the weather head, that is a fairly recent event. Prior to that the POCO here supplied everything up to and including the meter socket and retained ownership of all those items. And they repair them for free. I do have one service with the SE cable in the condition in your photos. The insulation on the two insulated conductors appears to be fine. While the insulated conductors are more exposed to weather with the outer covering gone, the proximity of the line conductors to the service neutral is as it always has been. And the ends of the insulated wires projecting from the weather head are always exposed to the Sun anyway. I see no special hazard. Do all your neighbors want one like it-for the good looks?

    Bookmark   May 11, 2012 at 7:39PM
Sign Up to comment
More Discussions
Please Critique Low-Volt (Home Automation) Plan/Proposal
GW/Houzz Community, As always, I want to thank this...
Andrew K.
Motion sensor that doesn't click
I have a motion sensor very much like the picture attached...
drmeow3
How to get garage freezer to work in cold weather
I have a 7-year-old GE refrigerator/freezer in my unheated,...
amyf5
Reuse electrical panel
I replaced a 24 circuit Square D panel with a new 40...
zver11
Insulation in electrical box
While in my attic the other day I saw an open electrical...
sgilliatt
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™